UTS10BI seems to cause a fault on my UPS inverter

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UTS10BI seems to cause a fault on my UPS inverter
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:46 PM . Last Modified: ‎2024-03-20 01:04 AM

0 Likes
5
1612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:46 PM . Last Modified: ‎2024-03-20 01:04 AM

UTS10BI seems to cause a fault on my UPS inverter

I just installed my UTS10BI and tested the UPS by throwing the main breaker.

The UTS switches to UPS, the UPS flashes the overhead lights for a brief second, then throws a fault & resets itself. The UTS powers off completely, the UPS resets itself, the UTS powers back on, the overhead lights flash, the UPS faults & the cycle goes on & on.

I tested the UPS as a standalone with just a light bulb plugged into it & it works fine.

If I have nothing turned on in the house, the UPS does not throw a fault, the UTS powers ok & switches all the "either" circuits just fine and then I can turn on the house lights and it seems to work.

I did think of something this morning that I will try. I have the UPS Surge Overload Time set to 1 second. I will set it to Zero & see if that makes a difference. The UTS setting for the UPS is 1800 watts.

I have a Royal Inverter PIC2000 modified sine wave (2000 watts) with a 100 amp hour 12 volt deep cycle battery.

Does the UTS need a pure sine wave inverter?

Thanks for your help.

-Todd

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • battery
  • help
  • inverter
  • test
  • testing
  • ups
  • uts10bi
  • uts6
  • uts6bi
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:46 PM . Last Modified: ‎2024-03-20 01:04 AM

0 Likes
0
1612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:46 PM . Last Modified: ‎2024-03-20 01:04 AM

Thx, will the prosine handle the inrush?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:46 PM . Last Modified: ‎2024-03-20 01:04 AM

0 Likes
0
1612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:46 PM . Last Modified: ‎2024-03-20 01:04 AM

I tried setting the ups surge overload to zero.
It didn't seem to change in the results.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:46 PM . Last Modified: ‎2024-03-20 01:04 AM

0 Likes
0
1612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:46 PM . Last Modified: ‎2024-03-20 01:04 AM

i asked our UTS product expert who had several questions to try and figure out what is happening:

• Where is the PIC2000 plugged into during normal operation?
• How many outlets do you have set for "either" and also whether you have any set for "uninteruptible?"
• are the lights incandescent or fluorescent?
• are the lights on their own independent circuit?

It sounds as if the UPS/Inverter is becoming overloaded because without power from the UPS or any other source during a blackout or test, the UTS User interface will turn off - at this time, are suspecting the overload is likely related to the inrush.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:46 PM . Last Modified: ‎2024-03-20 01:04 AM

0 Likes
0
1612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:46 PM . Last Modified: ‎2024-03-20 01:04 AM

Warning, long winded gibber jabber approaching below...

The pic2000 is plugged into the convenience outlet on the UTS.

No circuits are set to "uninterruptible"

These are the circuits set to "either"

2-Cloths Washer & lights, set as "lights" on the UTS
4-garage door, lights, & plugs in living room set as "garage"
6-19 inch kitchen tv & microwave, set as "microwave", but no microwave plugged in yet.
7-lights & plugs, smoke detector, set as "lights"
8-Masterbedroom & Masterbath, lights & plugs, 46 inch LED 90 watt TV, Bose speaker system, 2 DVRs, blu-ray player, 2 alarms clocks, 1 electric shaver, set to "home theater" & "either" because I have a small APC BE350G UPS that the DVRs & the alarm clocks are plugged into that carry the DVRs until the UTS's UPS kicks in.

All lights are CFL bulbs.

B4 I throw the main breaker, those 5 circuits only show less than 100 watts between the 5 on the UTS.

If I use the PIC2000 solo (not plugged into the UTS) & plug a vacuum into it, the vacuum runs fine, runs in bypass mode while being plugged into mains, I unplug it from mains, the pic2000's own internal 10 millisecond 30amp transfer switch flips it from mains to inverter, the vacuum starts to shut down for a flash & then picks back up & is running on the 12v deep cycle. (1200 watts inrush)

It kind of sounds like inrush is causing the fault because if I have less then 100 watts asking for power at the time of the UTS switch from mains to UPS it works fine. If I have 3 or 4 lights on i.e. more then 100 watts asking for immediate power then the pic2000 throws the fault. But it doesn't make sense to my tiny brain why the pic2000 works fine as a stand alone with the vacuum asking for 1200 watts of immediate input, but not with the UTS when only asking for 150 watts of inrush power.

Thank you so much for the help!

By the way, my APC BE350G is not happy with the modified sine wave, nor is my smoke detector. The BE350 makes a buzz noise about every half a second or every second almost like a heart beat. I think I may go to a pure sine wave inverter.

Any recommendations on a pure sine wave inverter/charger at least 1000 watts that will use a 12v deep cycle group27 battery?

There seems to be so many inverter choices it's confusing to a simpleton like me to know what's a good one to get.

Of course ultimately it would be nicest to get the pic2000 working.

You folks are Great!!!

-Todd

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:46 PM . Last Modified: ‎2024-03-20 01:04 AM

0 Likes
0
1612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:46 PM . Last Modified: ‎2024-03-20 01:04 AM

i asked around again and we are thinking that it is possibly an inrush issue based on your new information or possibly a combination of step approximated sinewave with the CFLs as well.

Fluorescent bulbs - although they use low wattage nominally, have ballasts that are used to ignite the gases for illumination. All of them operating together could be causing the overload. i can't say we have specifically tested the CFLs with the UTS where I am at though.

also, Xantrex is a Schneider Electric company. it was suggested you take a look at something from their True Sinewave line maybe?

http://www.xantrex.com/power-products/power-inverters/overview.aspx

http://www.xantrex.com/power-products/power-inverters/prosine.aspx

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:46 PM . Last Modified: ‎2024-03-20 01:04 AM

0 Likes
0
1613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:46 PM . Last Modified: ‎2024-03-20 01:04 AM

Thx, will the prosine handle the inrush?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore