Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Posted: 2021-06-29 06:02 PM . Last Modified: 2024-03-21 03:59 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:02 PM . Last Modified: 2024-03-21 03:59 AM
This is my first post here. I'm hoping someone can give me some guidance.
Last year we installed a UTS10BI in my friends house. The unit has never needed to be used but if it did it would have been connected to a portable generator which would reside outside and would be connected if the power were to go out.
All of the circuits are fairly typical circuits you would want powered up.
Here's the list.
Livingroom Outlets and lights 15A
Kitchen Outlets 20A
Bathroom Outlet 20A
Fridge Outlet 20A
Bedroom Outlet and lights 20A
Sump Outlet 20A
Garage Outlet 20A
Furnace Outlet 20A
Hot Water Heater 20A
Hot Water Heater 20A
They had no hot water so they called a plumber who told them to call me. So I went up to have a look thinking it would be the heating element in the HWH, but it turned out the 9/10 circuit would not reset on the APC. I did some testing and then noticed this:
49qTzA%2F1ytfB5YG4UV5BMg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg
Once I noticed this I really started looking at the circuit board as I now was very concerned for my friends family as I know this type of wire burning can lead to a real fire. Thankfully the APC is tripping out so it was protecting itself as it should be... but it was still a heavy concern. As I dug deeper I discovered this:
bv%2Fcwus05ZQU5xCgEqtJ5A%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
So at this point I made the decision to pull the unit offline completely. For safety I replaced the dual 20A breaker in the breaker box to be sure it was good and safe. I also pulled all the circuits off the APC as I have no idea what would have caused this type of failure. I've installed a few of these including one in my parents house that has worked flawlessly for years both under standby and full load modes.
So if anyone can give me an idea as to what would have casued this type of failure that would be greatly appreciated. I've been working with electrical systems for a long time and cant wrap my head around how this could happen. My knee jerk was that the heating element was drawing high amperage for to long and cooked the board but the HWH has been working fine since I pulled it off the APC, hot water all weekend, no problems.
So it seems to me that the failure is on the board. But I would like more opinions on the matter.
Thanks in advance for any help.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:03 PM . Last Modified: 2024-03-21 03:59 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:03 PM . Last Modified: 2024-03-21 03:59 AM
after seeing this posting am totally scared to buy this product. However, it just could have been a manufacturing defect. ..if it happens again then its a poor design.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:02 PM . Last Modified: 2024-03-21 03:59 AM
Hi John,
I will discuss this with our engineering team and come back to you tomorrow with additional detail and steps to take. We appreciate the great photos and information you've provided so far. Is it possible for you to provide me the serial number of the UTS10BI for reference? At a minimum, just the first (6) characters will do if you prefer to not share the whole thing publicly.
I am sorry to hear that you and your friend's family had to go through this due to the problem with the UTS.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:03 PM . Last Modified: 2024-03-21 03:59 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:03 PM . Last Modified: 2024-03-21 03:59 AM
Hi John,
If it is okay with you, I'd like to have someone contact you from our support team to set up a return of that unit to us for review and give you a replacement even though it is out of warranty. If it's okay, we'll use the email configured in your profile here to touch base.
In addition to setting that up and to help with a review of the unit, we have some questions we'd like to ask as part of that regarding the load, especially that water heater.
Essentially questions are along the lines of:
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:03 PM . Last Modified: 2024-03-21 03:59 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:03 PM . Last Modified: 2024-03-21 03:59 AM
That would be fine Angela, that is my work email. I appreciate the help. I just have no idea what could have caused it, other than a short, but it seems weird that both the circuits would short out at the same time... which is why I replaced the circuit breaker even thought it worked and tested out fine, but since that was the only thing I would think that could cause it I replaced it to be safe.
My answers in bold.
I appreciate all the help regarding this.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:03 PM . Last Modified: 2024-03-21 03:59 AM
You're welcome. I'll let support work with you further (as to not have two separate people asking you stuff) on details requested to help identify what caused the issue and then we can loop back here at the end and post a summary of what is found.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:03 PM . Last Modified: 2024-03-21 03:59 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:03 PM . Last Modified: 2024-03-21 03:59 AM
Sounds great thank you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:03 PM . Last Modified: 2024-03-21 03:59 AM
On 7/9/2015 12:54 PM, Angela said:we can loop back here at the end and post a summary of what is found.
Hi John and Angela,
As another owner of a UTS10BI (and designer of electronics and PCBs) I look forward to the results of this investigation.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:03 PM . Last Modified: 2024-03-21 03:59 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:03 PM . Last Modified: 2024-03-21 03:59 AM
after seeing this posting am totally scared to buy this product. However, it just could have been a manufacturing defect. ..if it happens again then its a poor design.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.