Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Please select a country to continue with beta search.
Posted: 2021-06-30 12:03 AM . Last Modified: 2024-03-20 12:28 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:03 AM . Last Modified: 2024-03-20 12:28 AM
Hello -
My UTS10BI is all hook uped. I understand selecting a non interruptable circuit - having the UPS for a secondary backup to the generator. However - before I spend $500+ on a UPS - I am searching for the answer to to the following question.
If I DO NOT have a UPS - and my power goes out - will my UTS10BI loose all of its circuit settings - because there is no power to it (until I hoop up the generator)???
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:03 AM . Last Modified: 2024-03-20 12:28 AM
The settings would be saved in the UTS so you won't have to reset it all the time. I guess the EEPROM settings are actually backed up by capacitors (which if the UTS is left in storage for years, well they might dry out). The UPS was actually introduced originally when we were going to provide auto-start function of the generator. So while the generator was starting, the UPS would back up the UTS or the circuit you wanted as uninterruptable. We never offered the auto-start though because of changes in compliance and local standards preventing this type of thing I think. I think Honda might with the UTS6H though.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:03 AM . Last Modified: 2024-03-20 12:28 AM
The settings would be saved in the UTS so you won't have to reset it all the time. I guess the EEPROM settings are actually backed up by capacitors (which if the UTS is left in storage for years, well they might dry out). The UPS was actually introduced originally when we were going to provide auto-start function of the generator. So while the generator was starting, the UPS would back up the UTS or the circuit you wanted as uninterruptable. We never offered the auto-start though because of changes in compliance and local standards preventing this type of thing I think. I think Honda might with the UTS6H though.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.