UPS won't switch from battery to generator.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS won't switch from battery to generator.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
110
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
zuhnc
zuhnc
Cadet

Posted: ‎2025-09-25 08:09 PM . Last Modified: ‎2025-09-25 08:24 PM

0 Likes
3
143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-25 08:09 PM . Last Modified: ‎2025-09-25 08:24 PM

UPS won't switch from battery to generator.

I have multiple APC UPS's. All of them except the BackUPS 1000 will run on my generator. Onan 15KW gaseous generator, electronic governor for 60Hz (+/- 1/2 Hz), and electronic voltage regulator to keep voltage +/- 5V of 120/240 under any load.  Normal load on generator is less than 3 KW.

Parameters on UPS set at widest limits.  Unit shuts down after two minutes under any condition.  UPS configured to not initiate any shutdown.

 

Edit:  Battery is less than 4 months old.  Replaced due to UPS overcharging the first battery, which was only 9 months old.  UPS passes "self-test", according to the logs.

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Spock Teken
Spock

Posted: ‎2025-09-26 02:50 AM

0 Likes
0
138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-26 02:50 AM

The APC Back-UPS Series is well known to react poorly when on generator power if the output isn’t clean when compared to the POCO.

 

You may refer to this APC Resource Link:

 

https://www.se.com/us/en/faqs/FA158842/

 

A basic validation is to measure the output while on generator power at different locations using a calibrated and certified oscilloscope / power quality analyzer.

 

In the ideal situation nothing would be on and powered. At this point you would connect the Back-UPS to the outlet and monitor its behaviour.

 

If the Back-UPS operates as intended than add more loads to the building. You’ll quickly see the Back-UPS will switch over to battery only mode.

 

Ask yourself why??

 

NOTE: You can not simply rely on measuring the voltage / frequency as the final determination. 

Questions Ask . . . 👍 

Reply

Link copied. Please paste this link to share this article on your social media post.

zuhnc
zuhnc
Cadet

Posted: ‎2025-09-26 06:13 AM

0 Likes
1
112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-26 06:13 AM

What does this mean - " if the output isn’t clean when compared to the POCO."?  The load on the generator is less than 2KW, and the UPS load is 30%.  The waveform of the generator looks identical to that of my POCO.

 

Can a firmware upgrade remedy this?  Is one even available?

 

The issue is the UPS doesn't even TRY to go back to supplied power, and instead ALWAYS shuts everything down after 2 minutes, regardless of settings.  Is this normal?

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2025-09-29 04:48 AM

In response to zuhnc
0 Likes
0
110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-29 04:48 AM

There are no user available firmware on the Back-UPS Series. As it relates to the power output from your generator it’s obviously not clean.

 

Meaning it’s generating dirty power which the Back-UPS doesn’t like. That can span from voltage, frequency, sine wave, THD, etc.

 

The litmus test is the fact the Back-UPS operates fine while AC power is provided by the POCO. It obviously doesn’t operate fine while on generator as such the output is not 1:1 in terms of power quality.

 

In the vast majority of times when it’s not voltage / frequency the primary reason is 3rd harmonic THD.

 

If you have any high quality filters available you can affirm & test this theory out. 

Using a scope would also show how much and the range of frequencies being generated by your Onan.

 

Lastly, if the system is connected to a computer running APC Power Chute. Provide the following logs for review: Event, Data, UPS during the time the system is on generator power.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore