Posted: 2025-09-25 08:09 PM . Last Modified: 2025-09-25 08:24 PM
I have multiple APC UPS's. All of them except the BackUPS 1000 will run on my generator. Onan 15KW gaseous generator, electronic governor for 60Hz (+/- 1/2 Hz), and electronic voltage regulator to keep voltage +/- 5V of 120/240 under any load. Normal load on generator is less than 3 KW.
Parameters on UPS set at widest limits. Unit shuts down after two minutes under any condition. UPS configured to not initiate any shutdown.
Edit: Battery is less than 4 months old. Replaced due to UPS overcharging the first battery, which was only 9 months old. UPS passes "self-test", according to the logs.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-26 02:50 AM
The APC Back-UPS Series is well known to react poorly when on generator power if the output isn’t clean when compared to the POCO.
You may refer to this APC Resource Link:
https://www.se.com/us/en/faqs/FA158842/
A basic validation is to measure the output while on generator power at different locations using a calibrated and certified oscilloscope / power quality analyzer.
In the ideal situation nothing would be on and powered. At this point you would connect the Back-UPS to the outlet and monitor its behaviour.
If the Back-UPS operates as intended than add more loads to the building. You’ll quickly see the Back-UPS will switch over to battery only mode.
Ask yourself why??
NOTE: You can not simply rely on measuring the voltage / frequency as the final determination.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-26 06:13 AM
What does this mean - " if the output isn’t clean when compared to the POCO."? The load on the generator is less than 2KW, and the UPS load is 30%. The waveform of the generator looks identical to that of my POCO.
Can a firmware upgrade remedy this? Is one even available?
The issue is the UPS doesn't even TRY to go back to supplied power, and instead ALWAYS shuts everything down after 2 minutes, regardless of settings. Is this normal?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-29 04:48 AM
There are no user available firmware on the Back-UPS Series. As it relates to the power output from your generator it’s obviously not clean.
Meaning it’s generating dirty power which the Back-UPS doesn’t like. That can span from voltage, frequency, sine wave, THD, etc.
The litmus test is the fact the Back-UPS operates fine while AC power is provided by the POCO. It obviously doesn’t operate fine while on generator as such the output is not 1:1 in terms of power quality.
In the vast majority of times when it’s not voltage / frequency the primary reason is 3rd harmonic THD.
If you have any high quality filters available you can affirm & test this theory out.
Using a scope would also show how much and the range of frequencies being generated by your Onan.
Lastly, if the system is connected to a computer running APC Power Chute. Provide the following logs for review: Event, Data, UPS during the time the system is on generator power.
Questions Ask . . . 👍