Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

UPS for HTPC with Plasma TV

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS for HTPC with Plasma TV
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:51 AM . Last Modified: ‎2024-03-20 12:15 AM

0 Likes
3
2099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:51 AM . Last Modified: ‎2024-03-20 12:15 AM

UPS for HTPC with Plasma TV

I'm looking to accomplish 2 things for my home theater system.
1) Provide no more than 10 min. battery time for my PC. Actually just enough time to shut down the system automatically in the case of a power loss. The PC wouldn't draw more than 250w.
2) Provide clean power (AVR) to all/or most components in my home theater system. Components include a 50" Plasma TV (480w), Sony receiver (270w), satellite box and the PC.
My thought would be to plug the PC in a battery/surge outlet and the TV into a surge only outlet. The remaining receiver and satellite box could be plugged into surge only outlets if that's possible without adding significant UPS requirements. The PC and TV are my main concerns. (I can plug the receiver/satellite box in a simple power surge bar if necessary.)
I'm presently using a couple of APC Battery Backups 750's on computer installations. Would UPS units such as these handle my home theater requirements? If not, what will I need?
Thanks in advance for any help.

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:51 AM . Last Modified: ‎2024-03-20 12:15 AM

0 Likes
0
2099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:51 AM . Last Modified: ‎2024-03-20 12:15 AM

Thank you both for this information.
If I choose a single unit solution, can either the APC AV 1kVA S Type Power Conditioner or APC Smart-UPS 1000VA handle my system? Do the specifications at approximately 700W/1000VA mean that I couldn't/shouldn't plug in more than the computer and TV, considering that's approximately the maximum wattage rating for these 2 components. Can either of these two APC units actually handle having all my components plugged into them without overload? Anything beyond the 2 mentioned units will be outside my budget.

Thank you for any additional insight.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:51 AM . Last Modified: ‎2024-03-20 12:15 AM

0 Likes
0
2099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:51 AM . Last Modified: ‎2024-03-20 12:15 AM

I posted here and between the information "i picked a winna" gave and the research on the home theater protection issue I did online I was able to decide what HT protection I wanted. Have you looked at APC AV line here https://www.apcc.com/products/apcav/products/ ? From the info I read PC surge protection with battery backups units should not be used for home theater protection. Depending on your budget and type of protection you want ACP AV products give you enough options for surge protection and surge protection with battery back up for your HT setup. I also use APC Battery Backup 750s for my computers and am pleased with their performance. If a PC was part of my HT system I would have an electrical run dedicated to each and run a 750 for the PC and an AV unit for the home theater.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-30 03:51 AM . Last Modified: ‎2024-03-20 12:15 AM

0 Likes
0
2099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:51 AM . Last Modified: ‎2024-03-20 12:15 AM

i'd agree with mary. you have quite an upscale system and i would look at something in the APC AV line. all the APC AC UPSs have AVR where as the BE750G's or BE750BB UPSs do not. i would recommend against an UPS that outputs a step approximated sinewave (which includes any Back UPS product or the J type AV UPSs) as well becuse a lot of upscale equipment, especially the PC power supply, may require a pure sinewave to function properly and may reboot or drop upon the UPS switching to battery back up power. if you have a smaller budget, you can look into something like a smaller Smart UPS which has all battery and surge protection outlets as well as outputs a pure sinewave.

it all depends what you want - the regular UPSs are meant to go under desks, in server rooms, etc and arent aesthetically pleasing where as the AV UPSs offer nicer front displays with more information and are aesthetically pleasing but cost a bit more.

let us know if you have any questions!

[Smart UPS|http://apc.com/products/family/index.cfm?id=165]

[APC AV Products|http://apc.com/products/category.cfm?id=15]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:51 AM . Last Modified: ‎2024-03-20 12:15 AM

0 Likes
0
2100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:51 AM . Last Modified: ‎2024-03-20 12:15 AM

Thank you both for this information.
If I choose a single unit solution, can either the APC AV 1kVA S Type Power Conditioner or APC Smart-UPS 1000VA handle my system? Do the specifications at approximately 700W/1000VA mean that I couldn't/shouldn't plug in more than the computer and TV, considering that's approximately the maximum wattage rating for these 2 components. Can either of these two APC units actually handle having all my components plugged into them without overload? Anything beyond the 2 mentioned units will be outside my budget.

Thank you for any additional insight.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore