I was wondering if it would be feasible to add a voltage regulator like the Line-R products between a non sine wave UPS and the power supply of a PC. It seems that this would be cost effective if one could not afford a sine wave UPS. Like me. 🙂
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-25 11:10 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-25 11:10 PM
No. An AVR between the UPS and the PSU will detect the approximated sinewave as a wave distortion and will try to unnecessarily regulate the output voltage coming out the UPS. The AVR would start switching it's internal relays like crazy making a lot of clicking noises and intruducing more distortion to an already distorted wave.
Message was edited by: The Notorious K.M.P.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-25 11:10 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-25 11:10 PM
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-25 11:10 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-25 11:10 PM
No. An AVR between the UPS and the PSU will detect the approximated sinewave as a wave distortion and will try to unnecessarily regulate the output voltage coming out the UPS. The AVR would start switching it's internal relays like crazy making a lot of clicking noises and intruducing more distortion to an already distorted wave.
Message was edited by: The Notorious K.M.P.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of