I was wondering if it would be feasible to add a voltage regulator like the Line-R products between a non sine wave UPS and the power supply of a PC. It seems that this would be cost effective if one could not afford a sine wave UPS. Like me. 🙂
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-25 11:10 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-25 11:10 PM
No. An AVR between the UPS and the PSU will detect the approximated sinewave as a wave distortion and will try to unnecessarily regulate the output voltage coming out the UPS. The AVR would start switching it's internal relays like crazy making a lot of clicking noises and intruducing more distortion to an already distorted wave.
Message was edited by: The Notorious K.M.P.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-25 11:10 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-25 11:10 PM
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-25 11:10 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-25 11:10 PM
No. An AVR between the UPS and the PSU will detect the approximated sinewave as a wave distortion and will try to unnecessarily regulate the output voltage coming out the UPS. The AVR would start switching it's internal relays like crazy making a lot of clicking noises and intruducing more distortion to an already distorted wave.