UPS 650 - Trouble After Electrical Fault in Building

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS 650 - Trouble After Electrical Fault in Building
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-22 03:19 AM

0 Likes
6
1817
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-22 03:19 AM

UPS 650 - Trouble After Electrical Fault in Building

Each one of our computers has its own APC UPS 650. A faulty piece of equipment was plugged into an outlet. There was a spark, but the 20-amp circuit breaker on the 200-amp panel didn't trip.

Two computers were on at the time. The UPS for both computers beeped and clicked (going to battery), but both computers shut down. (Both computers were disconnected from the UPS before I could check whether the computers were plugged into Battery Back-Up or accessory only.) There were no noises from any of the UPS connected to the computers that weren't on at the time.

When both of the shut-down computers were turned on again, the "safe mode" screen came up. Re-started Windows normally, and all OK.

Then, the moron plugged the same faulty piece of equipment into the same outlet again. Just like the first time, the 20-amp circuit breaker didn't trip, and both UPS beeped and clicked, and the computers shut down.

But this time, when the computers were turned on again, the UPS beeped and clicked. The "safe mode" screen came up, but Windows didn't boot up in "load normal" mode. Both computers went to blue screen and turned off.

Turned both computers on again. More beeping and clicking from UPS. Windows didn't boot up in safe mode. Went to blue screen, but computers didn't turn off.

One more try. Turned both computers on again. Beeping and clicking from UPS. Both computers went right to blue screen, but didn't turn off.

Hard drives are OK -- tech ran chkdsk /r in shop. (Whew!) But I can't figure out if the UPS are OK.

The green lights on the front are ON and steady. When I press the Test button on the front, there's one long beep. Neither Site Wiring Fault light on the back was ever on.

I can't tell if the Overload Protector buttons are out or not. The center bars aren't flush with the housing, but they protrude maybe 1/16", not 1/4" as indicated in the specs. I can push them in, to be flush with the housing, then they pop back out to protrude the 1/16" as before.

Both computers are 5-year-old Dell Dimension 2400, 2.4GHz Pentium 4.

What the heck happened -- why did the UPS beep and click when the computers were turned on, for example? Should we put the UPS back in service?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • back-ups
  • beeping
  • shutdown
  • ups
  • windows
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:29 AM . Last Modified: ‎2024-03-22 03:18 AM

0 Likes
0
1816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:29 AM . Last Modified: ‎2024-03-22 03:18 AM

Sorry, no, your answer was not helpful to me. But I understand that helping me isn't your objective. Helping APC sell more product is your objective, and in that, you may indeed have been helpful.

I sent an email through the APC online support system at the same time that I posted in this forum. The reply to my email helped me determine that the batteries are dead.

Never got answers to my other questions, of course, since answering those questions would have required actually reading and understanding my questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-22 03:19 AM

0 Likes
0
1816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-22 03:19 AM

H.Goodman,

Typical battery life is three to five years. I notice that your unit is 8 years old. So I think that the battery in the unit is no longer in good condition to provide power during power problems. You may force the UPS to work on battery by unplugging it from the wall to check if the unit provides power on battery mode.

If it does not provide power to the equipment on battery, then the battery may needs to be replaced. However, I would just trade in this old unit to a new unit.
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=298

I hope that this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:29 AM . Last Modified: ‎2024-03-22 03:19 AM

0 Likes
0
1816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:29 AM . Last Modified: ‎2024-03-22 03:19 AM

Model: BK650MC
Serial: PB0112124417
Batteries have never been replaced.
Since first posting, I've learned that the computers were plugged into Battery Back-Up, not accessory only.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 01:29 AM . Last Modified: ‎2024-03-22 03:19 AM

0 Likes
0
1816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:29 AM . Last Modified: ‎2024-03-22 03:19 AM

H. Goodman,

I think that the UPS transferred to battery due to power problems on the line, and then It might not have had the battery charge to provide power to the Computer when it transferred to battery mode. This may occur if the unit has got a bad battery.However, let me gather some more information from you to provide you an insight.

Mode and Serial number of the two UPSs. You can find these details on a white bar code sticker at the rear.
Have the batteries ever been replaced in these units?
Were the Computer and Monitor plugged into the battery backup outlets?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:29 AM . Last Modified: ‎2024-03-22 03:18 AM

0 Likes
0
1816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:29 AM . Last Modified: ‎2024-03-22 03:18 AM

Thanks for your reply, but you didn't answer my questions.

I have the UPS disconnected from the computer that it didn't protect, of course, and there's no equipment attached to it, since I can't trust that the UPS won't damage equipment that's connected to it.

The UPS is plugged in, and the green light is ON, and there's no beeping or clicking. When I unplug the UPS, there's one long beep, then a short beep every five seconds.

Does this mean that the battery is good, or not? If the battery isn't good, why isn't there a "Battery Failure" light on the UPS, to warn users that it's time to replace the battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 01:29 AM . Last Modified: ‎2024-03-22 03:18 AM

0 Likes
0
1816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:29 AM . Last Modified: ‎2024-03-22 03:18 AM

Okay, if the unit does not provide the expected runtime after 3 or 5 years of use, then that is the indication of the Bad Battery for this unit. The battery run time can be checked by pressing and holding the "Test" switch and waiting to see how long the UPS provides power to the equipment before the low battery warning is sounded.

Press the "Test" portion of the Test/Alarm Disable Switch to simulate a power outage - the UPS battery
supplies power to the equipment.

The UPS runtime can be seen in the UPS user manual. Click on the below link to download the UPS user manual.
[http://www.apcmedia.com/salestools/ASTE-6Z7UZ8_R0_EN.pdf]

Unfortunately, this old model does not have a separate Replace Battery Indication. For your information, the current UPSs will indicate the users if the battery is bad.

I hope that this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:29 AM . Last Modified: ‎2024-03-22 03:18 AM

0 Likes
0
1817
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:29 AM . Last Modified: ‎2024-03-22 03:18 AM

Sorry, no, your answer was not helpful to me. But I understand that helping me isn't your objective. Helping APC sell more product is your objective, and in that, you may indeed have been helpful.

I sent an email through the APC online support system at the same time that I posted in this forum. The reply to my email helped me determine that the batteries are dead.

Never got answers to my other questions, of course, since answering those questions would have required actually reading and understanding my questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore