System turns off even with UPS

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • System turns off even with UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:21 AM

0 Likes
10
9837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:21 AM

System turns off even with UPS

Hello, I have APC BACK-UPS ES 650VA 230V INDIA Offline UPS with software, Cooler Master eXtreme Power Plus 700W PSU both under warranty. My computer runs for 20+ hours per day.

UPS Output Power Capacity : 390W

Typical recharge time : 5 hours

Situation #1 (Works fine)

Load on Battery Backup : 100-130W

UPS switches to battery backup and provides the given mins of uptime without any problem.

Tested in random over-voltage/blackouts/fluctuation events as well as in manual blackout testing.

Situation #2 (Problem)

Load on Battery Backup : 300+W but < 390W

UPS switches to battery backup but sometimes computer turns off immediately in any event like there was no ups installed.

Now the reasons can be

1) Battery is exhausting in split second.

2) Battery was not charged completely.

3) My power supply is faulty and its loosing the charge before the switching occurs / UPS is switching after my power supply looses its charge on load.

I am using APC Powerchute software. The software has High voltage sensitivity selected, it shuts down the computer when battery backup has <=5 mins remaining (all default values).

Now this software shows that i have 100% charged batteries, battery passed its self test showing batteries are working normally.

But sometimes when the load is more than 300W, even a small fluctuation restarts my computer.

So now -

If batteries are getting exhausted in split second then the software should show the changed battery value on next restart but it shows 80-90% charged.

If battery wasn't charged completely then their software should reflect that low charge value OR computer should turn off in few mins in manual test (turning main switch off and let my computer run on battery backup).

If my power supply is faulty then it should turn off my computer in any case on any load, but it works without problem when load is low (<300W) and sometimes gives problems on high load (300w+). However i am not sure about capacitors charge holding time on load in my PSU.

I told my problem to APC Service Executive since these problems started to happen after connecting UPS (wasn't happening before this ups). The dude says to turn off your equipment and UPS and let the UPS charge from ac power source for 5 hours, many software shows wrong values (including their own apc powerchute).

Its an offline UPS, my computer runs for 20+ hours , software shows 100% battery time as well.

So where is the problem? PSU or UPS or something else?


Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

0 Likes
0
9835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

We'd recommend a larger VA UPS (option 2) - something like a 1500VA unit. If nothing else prevails, keep in mind you can trade that one in if you'd like towards a discount on a newer one.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

0 Likes
0
9835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

What does the UPS report the runtime as during situation #2 before you initiate the test? Do you ever hear any tones or see any LEDs during situation #2? I assumed you would've noted it but just checking.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

0 Likes
0
9835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

I cant see the runtime because system immediately restarts if any power related problems occur in that time, but at 310-320W runtime is 10mins. As system turns off and on, ups goes on battery mode till ac power source comes back on. Idle usage is 97-130W.

This has happened before but on rapid fluctuations and every time it was on high load. But while testing with manual blackout on high load, computer turned off as soon as i switched off the main source and ups went on battery mode.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

0 Likes
0
9835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

Its not exactly reboot as well, it literally cuts the power then starts it, there is a small delay in between which is higher than normal reboot. This has happened before few times but on rapid fluctuations and every time it was on high load. But while testing with manual blackout on high load, computer turned off as soon as i switched off the main source and ups went on battery mode. Sorry i edited that post as well. Is it possible that switching is taking more time on high load?

I will try to brain dead it and perform a second test by plugging random electrical items so that load goes above 350w.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

0 Likes
0
9835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

Oh ok - yes I was just looking for you to check at very high load assuming a power problem did not occur all of the time.

I don't suppose it is possible to put another high load on it besides your computer and see what happens with no data cable attached and maybe with it attached? Just to see if you can narrow it down to the computer or UPS? I can't really tell either what's happening.

My gut tells me that the runtime is close to 5 minutes (assuming you've chosen to keep your computer as long as possible and selected the lowest value of 5 minutes) and this it starts shutting down but it does not necessarily explain the reboots which I think basically what you're thinking - there is no one single symptom that confirms the UPS is at fault or the PSU in your PC is either.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

0 Likes
0
9835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

Ok i have tested ups with random electric equipment but i wasn't able to get load that high. I tested with a desk fan on high speed, a netbook, a dual emergency rechargeable light. After switching the main power off, fan changed its speed but netbook & light didnt loose power. Ran my computer without ups on high load, no problem as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

0 Likes
0
9835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

I consulted with a few folks here and they suggested this could be an issue with a Power Factor Corrected PSU or the transfer time causing this. It was suggested that I have you review knowledge base article FA158939 @ http://www.apc.com/site/support/index.cfm/faq/ and see what your feedback is on after reading that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

0 Likes
0
9836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

This can be the cause, here is a link to my PSU http://www.coolermaster-usa.com/product.php?product_id=2991

So my options are :

1) Replace my PSU with lower one.

2) Replace my UPS with higher one.

3) Reduce the load on my current PSU.

Currently i have removed my monitor from battery backup to surge protection slot to reduce the load. Which option would you suggest?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

0 Likes
0
9836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

We'd recommend a larger VA UPS (option 2) - something like a 1500VA unit. If nothing else prevails, keep in mind you can trade that one in if you'd like towards a discount on a newer one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

0 Likes
0
9836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

1500VA is extremely costly and way out of my budget, will 1000VA be sufficient? its a home desktop system and my highest power usage will be like 450W, 150w for future expansion.

There are 2 products available for 1000VA:

APC Back-UPS RS, 1000VA, 230V, INDIA

APC Power-Saving Back-UPS Pro 1000 with LCD, 230V, India

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

0 Likes
0
9836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:58 PM . Last Modified: ‎2024-03-21 01:20 AM

I asked our Back UPS support specialist and he suggested 1500VA. As the knowledge base article suggests, your 700W power supply is capable of requiring 875W since it is Power Factor Corrected. Something like the BR1000G-IN only gives 600W still. You could still run into a problem under certain operating conditions I imagine - maybe not as often. We'd still recommend 1500VA for your best chance of no issues.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore