Surge protection options for outlets lacking ground? (for use during travel)

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Surge protection options for outlets lacking ground? (for use during travel)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:26 AM

0 Likes
6
3019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:26 AM

Surge protection options for outlets lacking ground? (for use during travel)

I often travel to developing countries, and it's not unusual that I encounter electrical outlets that don't have a plug for ground -- just 2 prongs, nothing more. In a lot of these places I know that safety isn't much of a concern, and as long as "it works" then it's good enough. I've been looking into single outlet surge protection solutions, such as the APC P1 (for 120V) and P1-GR (for 220V), but I've stumbled upon a good bit of information suggesting that surge protectors don't work properly if they aren't connected to a grounded outlet, which brings me here.

My primary concern is for my laptop, and I do see that APC has the SurgeArrest Notebook Pro PNOTEPROC8. Noticing that this is made for a 2-prong cord with no ground, I'm wondering if this would be a better solution for my laptop than using something like the P1, despite the fact that P1 has better specs, since the PNOTEPROC8 seems that it must be designed with no ground in mind. Ideally I'd like something with better protection though, and the ability to plug in other devices (smartphone), even if it means finding a slightly heavier, bulkier solution.

So, my question: Can anyone say definitively whether the majority of APC products which are designed for grounded outlets will offer protection when there is no ground connection? Do I have any option other than using the PNOTEPROC8? Would something like a plug adapter with built-in fuse offer any increase in protection?

Please feel free to be as technical as you like in your response, as I actually enjoy learning how this stuff works!

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:25 AM

0 Likes
0
3018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:25 AM

Thanks, Angela. For what it's worth, I do think the section in that page defining clamping voltage and pass-through voltage could be made more clear, perhaps with the use of better examples. It's made more confusing by the fact that APC calls the UL1449 330V rating the "effective clamping voltage rating" where others describe a "UL1449 let through rating" (which is often 330V), and then some sources say they're the same thing (i.e. the Wikipedia article on surge protection).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:26 AM

0 Likes
0
3018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:26 AM

Hi again,

Did some checking and here is the answer I got:

With the 2 prong configuration, you're only getting the normal mode protection and with the three prong, you are able to achieve both Normal mode and Common mode protection. So, yes, the surge protection would rate higher with the Common Mode normal mode configuration.

Hope that helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:26 AM

0 Likes
0
3018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:26 AM

I often travel to developing countries, and it's not unusual that I encounter electrical outlets that don't have a plug for ground -- just 2 prongs, nothing more. In a lot of these places I know that safety isn't much of a concern, and as long as "it works" then it's good enough. I've been looking into single outlet surge protection solutions, such as the APC P1 (for 120V) and P1-GR (for 220V), but I've stumbled upon a good bit of information suggesting that surge protectors don't work properly if they aren't connected to a grounded outlet, which brings me here.

My primary concern is for my laptop, and I do see that APC has the SurgeArrest Notebook Pro PNOTEPROC8. Noticing that this is made for a 2-prong cord with no ground, I'm wondering if this would be a better solution for my laptop than using something like the P1, despite the fact that P1 has better specs, since the PNOTEPROC8 seems that it must be designed with no ground in mind. Ideally I'd like something with better protection though, and the ability to plug in other devices (smartphone), even if it means finding a slightly heavier, bulkier solution.

So, my question: Can anyone say definitively whether the majority of APC products which are designed for grounded outlets will offer protection when there is no ground connection? Do I have any option other than using the PNOTEPROC8? Would something like a plug adapter with built-in fuse offer any increase in protection?

Please feel free to be as technical as you like in your response, as I actually enjoy learning how this stuff works!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:26 AM

0 Likes
0
3018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:26 AM

All of our surge units use a multi-layer approach to protect against power events, with a combination of MOV's, thermal fuses and capacitors. Units that have a ground wire, however, have an additional layer of protection by trying to shunt excess energy off to the ground. This is why you'll see surge equipment with a low "joule" rating (which makes a unit seem like it has weak surge suppression), but a low let-through voltage rating (which is the actual excess voltage that's passed through to equipment). There's an awesome knowledge base article written about this here: http://se-vl-167.ebusiness.schneider-electric.com:8226/support/index?page=content&id=FA158814&countr...

With that being said if you're going to be in a place without a ground wire accessible, the PNOTE would be a better choice for you. If you're using a surge unit that was designed to be grounded in a non-grounded application, you're not getting the full coverage the unit can offer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:25 AM

0 Likes
0
3018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:25 AM

Thanks for that. As for that knowledge base article, I'd love to read it but the link doesn't seem to work. Can you double check it?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:25 AM

0 Likes
0
3018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:25 AM

Try this -> What is the difference between the industry standards Joules and Let-Through Voltage? | FAQs | US

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:25 AM

0 Likes
0
3019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:05 AM . Last Modified: ‎2024-03-20 12:25 AM

Thanks, Angela. For what it's worth, I do think the section in that page defining clamping voltage and pass-through voltage could be made more clear, perhaps with the use of better examples. It's made more confusing by the fact that APC calls the UL1449 330V rating the "effective clamping voltage rating" where others describe a "UL1449 let through rating" (which is often 330V), and then some sources say they're the same thing (i.e. the Wikipedia article on surge protection).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore