Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Surge Protector

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Surge Protector
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
125
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

0 Likes
10
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

Surge Protector

Can someone recommend me best electricity surge protector for led tv? at my home the voltage seems to have issues all the time. One of my friend recommended me APC. TIA

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:27 AM . Last Modified: ‎2024-03-26 04:16 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:27 AM . Last Modified: ‎2024-03-26 04:16 AM

Hi Mark

If your measurements are correct, I would look at the Line-R products which give you automatic voltage regulation as well as surge protection.

Regards

Matt

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

On 9/27/2018 4:34 PM, John said:

Can someone recommend me best electricity surge protector for led tv? at my home the voltage seems to have issues all the time. One of my friend recommended me APC. TIA

You can trust on APC. They are the best for surge protection

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

I am currently living in Pakistan and the voltage level here I assumed raises to 270V which is not acceptable I guess and sometimes the voltage is very low.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

How have you measured the voltage?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

Through multimeter

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

It is unclear how this value was measured, and if it isn't just appearing to be 270V on a multimeter without true rms that is measuring a very distorted sine wave. I would suggest that you contact your electricity provider about this

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

On 9/27/2018 4:49 PM, John said:

It is unclear how this value was measured, and if it isn't just appearing to be 270V on a multimeter without true rms that is measuring a very distorted sine wave. I would suggest that you contact your electricity provider about this

I agree with your 100% I have planed to make better measurement, and if it is confirmed I will call the Electricity Provider... but I guess they will say: "this is normal, don't worry". So I wont to collect some information on how serious this is

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

On 9/27/2018 4:50 PM, Mark said:
On 9/27/2018 4:49 PM, John said:

It is unclear how this value was measured, and if it isn't just appearing to be 270V on a multimeter without true rms that is measuring a very distorted sine wave. I would suggest that you contact your electricity provider about this

I agree with your 100% I have planed to make better measurement, and if it is confirmed I will call the Electricity Provider... but I guess they will say: "this is normal, don't worry". So I wont to collect some information on how serious this is

Do you know any APC distributor in Pakistan as I don't know much about the country? I am just here for a short project

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

On , said:
On 9/27/2018 4:50 PM, Mark said:
On 9/27/2018 4:49 PM, John said:

It is unclear how this value was measured, and if it isn't just appearing to be 270V on a multimeter without true rms that is measuring a very distorted sine wave. I would suggest that you contact your electricity provider about this

I agree with your 100% I have planed to make better measurement, and if it is confirmed I will call the Electricity Provider... but I guess they will say: "this is normal, don't worry". So I wont to collect some information on how serious this is

Do you know any APC distributor in Pakistan as I don't know much about the country? I am just here for a short project

Check their reseller partner at apc website Also i think this website will fulfill your requirement http://www.w11stop.com/apc

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:26 AM . Last Modified: ‎2024-03-26 04:17 AM

On 9/27/2018 5:00 PM, John said:
On , said:
On 9/27/2018 4:50 PM, Mark said:
On 9/27/2018 4:49 PM, John said:

It is unclear how this value was measured, and if it isn't just appearing to be 270V on a multimeter without true rms that is measuring a very distorted sine wave. I would suggest that you contact your electricity provider about this

I agree with your 100% I have planed to make better measurement, and if it is confirmed I will call the Electricity Provider... but I guess they will say: "this is normal, don't worry". So I wont to collect some information on how serious this is

Do you know any APC distributor in Pakistan as I don't know much about the country? I am just here for a short project

Check their reseller partner at apc website Also i think this website will fulfill your requirement http://www.w11stop.com/apc

Thanks a lot for your support John.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:27 AM . Last Modified: ‎2024-03-26 04:16 AM

0 Likes
0
1245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:27 AM . Last Modified: ‎2024-03-26 04:16 AM

Hi Mark

If your measurements are correct, I would look at the Line-R products which give you automatic voltage regulation as well as surge protection.

Regards

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore