Smart UPS2200 shut down

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Smart UPS2200 shut down
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:40 PM . Last Modified: ‎2024-03-21 02:36 AM

0 Likes
6
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:40 PM . Last Modified: ‎2024-03-21 02:36 AM

Smart UPS2200 shut down

The last two mornings I have come to work the SmartUPS2200 has shut down the computer and all the lights on the UPS except the Load lights and the Battery level light are on. I have to turn off the UPS and then turn it back on. I find nothing in the log to indicate why it shut down. What's up?

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:41 PM . Last Modified: ‎2024-03-21 02:36 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:41 PM . Last Modified: ‎2024-03-21 02:36 AM

ok because if they are flashing, it indicates a relay weld which would require a UPS replacement unfortunately. the other scenarios with these LEDs would have sounds accompanied with them. generally this doesnt drop the load though like you are seeing.

different combinations of the center 6 LEDs scrolling can also mean a graceful shutdown but of course that doesnt make sense either.

it sounds like it may need to be replaced if there is nothing in the logs if you are sure about the LEDs being solid..

just a random thing, you dont have any random cables attached to the UPS on USB or the serial port do you? you should have ONLY USB or ONLY serial and definitely be using APC cables since others can cause weird issues.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:40 PM . Last Modified: ‎2024-03-21 02:36 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:40 PM . Last Modified: ‎2024-03-21 02:36 AM

hi

just to be sure - are these center 6 LEDs solid, scrolling, or flashing in unison? i assume there are no beeps or anything since you probably would have noted that as well.

let me know what the center 6 LEDs are doing specifically and i can help further. thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:41 PM . Last Modified: ‎2024-03-21 02:36 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:41 PM . Last Modified: ‎2024-03-21 02:36 AM

I had the same issue the night before so late yesterday afternoon I moved the batteries to another 2200 I have to see if the problem followed the batteries and it didn't. Had the unexpected shutdown again after swapping batteries. No beeps just solid lights.
I have two dell servers on it and both reported unexpected shutdowns at the same time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:41 PM . Last Modified: ‎2024-03-21 02:36 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:41 PM . Last Modified: ‎2024-03-21 02:36 AM

Ok I checked with the guy that restarted the UPS and he said all 6 lights were flashing with no sounds, guess I need to look at APC's trade in program and get another one on it's way.
Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:41 PM . Last Modified: ‎2024-03-21 02:36 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:41 PM . Last Modified: ‎2024-03-21 02:36 AM

yeah unfortunately that indicates a problem the boost/trim relay. so if the unit has been going to boost or trim mode overnight for a couple seconds or something, it is probably faulting out.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:41 PM . Last Modified: ‎2024-03-21 02:36 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:41 PM . Last Modified: ‎2024-03-21 02:36 AM

Solid if I recall correctly.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:41 PM . Last Modified: ‎2024-03-21 02:36 AM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:41 PM . Last Modified: ‎2024-03-21 02:36 AM

ok because if they are flashing, it indicates a relay weld which would require a UPS replacement unfortunately. the other scenarios with these LEDs would have sounds accompanied with them. generally this doesnt drop the load though like you are seeing.

different combinations of the center 6 LEDs scrolling can also mean a graceful shutdown but of course that doesnt make sense either.

it sounds like it may need to be replaced if there is nothing in the logs if you are sure about the LEDs being solid..

just a random thing, you dont have any random cables attached to the UPS on USB or the serial port do you? you should have ONLY USB or ONLY serial and definitely be using APC cables since others can cause weird issues.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore