Smart-UPS 750 (SUA750I) cuts power?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Smart-UPS 750 (SUA750I) cuts power?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:24 AM . Last Modified: ‎2024-03-22 04:06 AM

0 Likes
6
1539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:24 AM . Last Modified: ‎2024-03-22 04:06 AM

Smart-UPS 750 (SUA750I) cuts power?

Hi im running a desktop server pc with a p4 3.2ghz, a low budget graphics card and a raid controller with 10 drives connected. When the pc is in idle state, everything is fine (UPS load is 34.4%) but when i start some jobs on the server the UPS cuts power after 30-90 minutes. It immediately restores power but the server is shutdown hard. The UPS load when i ran the jobs is +- 40% which should be ok.

Is the server too heavy for this UPS? Or is the UPS broken?

Here is a screenshot from my datalog: http://i39.tinypic.com/bgdwye.jpg
its in idle state, then at 3:11 i start a job, and at 3:21 it cuts power.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:25 AM . Last Modified: ‎2024-03-22 04:06 AM

0 Likes
0
1540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:25 AM . Last Modified: ‎2024-03-22 04:06 AM

Yes, i use the USB connection, and yes when the server is idle not a problem, only when the load increases.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:24 AM . Last Modified: ‎2024-03-22 04:06 AM

0 Likes
0
1540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:24 AM . Last Modified: ‎2024-03-22 04:06 AM

how old is this? can you provide the first couple digits of the serial number? like JS0524?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:24 AM . Last Modified: ‎2024-03-22 04:06 AM

0 Likes
0
1540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:24 AM . Last Modified: ‎2024-03-22 04:06 AM

This is the serial # : QS0444141641, the batteries are 1.5 years old, the unit itself i dont know.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:24 AM . Last Modified: ‎2024-03-22 04:06 AM

0 Likes
0
1540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:24 AM . Last Modified: ‎2024-03-22 04:06 AM

interesting. am i right in saying you are using USB with this (versus a serial connection)? that noise you are hearing sounds like the output relay.

so this only happens when your load jumps up?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:24 AM . Last Modified: ‎2024-03-22 04:06 AM

0 Likes
0
1539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:24 AM . Last Modified: ‎2024-03-22 04:06 AM

do you hear any noises or see any LEDs flashing on the UPS? is the UPS itself rebooting where you see all the LEDs go off on the front and then it turns back on? or is it definitely just cutting the output power and then turning it back on, meaning the UPS itself is staying on the entire time?

can you show us what you see in the event log when this happens. the data log was helpful.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:24 AM . Last Modified: ‎2024-03-22 04:06 AM

0 Likes
0
1539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:24 AM . Last Modified: ‎2024-03-22 04:06 AM

i picKed a winna wrote:
or is it definitely just cutting the output power and then turning it back on, meaning the UPS itself is staying on the entire time?
Thanks for your reply,

Indeed, no leds are flashing, it just cuts the power output, the UPS itself stays online. When it does you hear a 'tick' and it restores it immediately.

Here is a screenshot of the event log, http://i41.tinypic.com/2zsy1s2.jpg
I ran a calibration test at 26/3 so it shows up at insufficient runtime avaible. Also i disconnected the UPS for now because of the power cuts thats why the software cant find the UPS model #

As you can see i've had 7 (seven!) power cuts in just a few days..

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:25 AM . Last Modified: ‎2024-03-22 04:06 AM

0 Likes
0
1541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:25 AM . Last Modified: ‎2024-03-22 04:06 AM

Yes, i use the USB connection, and yes when the server is idle not a problem, only when the load increases.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore