Smart Back-UPS - DataPort

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Smart Back-UPS - DataPort
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Janeway Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-20 03:11 AM

0 Likes
3
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-20 03:11 AM

Smart Back-UPS - DataPort

Good day,

I have a Smart Back-UPS 1200

Model Number BR1200GI

Serial number: 3B1424X02677

I am using the APC RS232 to DataPort cable. I would like to know if this UPS uses MicroLink or UPSlink. The reason being that I need it to work with Control4 Home Automation and their system will only work with a UPS that has UPSLink via the DataPort.

This UPS did ship with DataPort to USB connector but I managed to order online the DataPort to RS232 connection. The home automation has a driver that works with all UPSLink APC UPS's and allows one to understand when the UPS is offline (power lost) when it is restored, UPS load and when the UPS is about to die from battery depletion. The issue I have right now with a DataPort > RS232 > Home Automation is that regardless of the state - power off or power restored the UPS is returning the same information therefore I cannot determine if the signal I am getting, was due to power failure or restore. I cannot read any of the other values: Load, Last time power failed, UPS Initialize or Self Test. ALL APC UPS'S with UPSLink I can do this through DataPort > RS232 > Home Automation.

The first port of call is for me to determine from you if this UPS uses UPSLink or MicroLink.

If it is using UPSLink then could you give me the correct part number for a DataPort > RS232 cable for this UPS - I would like to check it against the part number I have. I have attached the bottom model and serial number of the UPS as an image to the post


Attachments
Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • datalog_cable_api
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-20 03:11 AM

0 Likes
0
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-20 03:11 AM

Hi,

The way simple signalling works is there is voltage either present or not present on specific pins. With this cable there would be voltage on DB9 pin 7 that is provided by the connected device. If UPS goes on battery there would be voltage passed to DB9 pin 8. If the UPS goes into a low battery state then there would be voltage passed to DB9 pin 1. For UPS turnoff voltage would be applied to DB9 pin 4 that would tell the UPS to power down.

I found a better schematic than what was presented in the apcupsd doc.

2598_pastedImage_0.png

Hope this helps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-20 03:11 AM

0 Likes
0
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-20 03:11 AM

Hi,

That cable is neither UPSLink or MicroLink. It is simple signalling. Simple signaling is the recognition of whether certain pins of the serial port are high or low, and allows for 3 states only; on battery, low battery and UPS turnoff.

You can find a wiring diagram at this link http://www.apcupsd.org/manual/manual.html#d-cable-wiring

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-20 03:11 AM

0 Likes
0
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-20 03:11 AM

Hi Bill,

Wow the first person after a lengthy process of emails and online chats that actually provided worth while help. Does it provide seperate signalling for off battery as well as on battery i.e. ability to determine when UPS fails over to batter due to power failure and comes back online due to power being restored?

UPS Turnoff I am assuming is when all the battery power is depleted? If so is there a short period of warning i.e. 1 minute before it completely runs out. Is there any API or RS232 information in order to interpreter these signals?

Thank you once again I really do appreciate this!!!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-20 03:11 AM

0 Likes
0
1135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-20 03:11 AM

Hi,

The way simple signalling works is there is voltage either present or not present on specific pins. With this cable there would be voltage on DB9 pin 7 that is provided by the connected device. If UPS goes on battery there would be voltage passed to DB9 pin 8. If the UPS goes into a low battery state then there would be voltage passed to DB9 pin 1. For UPS turnoff voltage would be applied to DB9 pin 4 that would tell the UPS to power down.

I found a better schematic than what was presented in the apcupsd doc.

2598_pastedImage_0.png

Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of