Sizing a new Back-Ups

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Sizing a new Back-Ups
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
116
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:57 PM . Last Modified: ‎2024-03-26 12:53 AM

0 Likes
2
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:57 PM . Last Modified: ‎2024-03-26 12:53 AM

Sizing a new Back-Ups

I need to buy a UPS for a home PC, and have come up with a question I hope someone here can answer.

The PC is pretty basic, nothing particularly high power. And I turn it off when I'm not using it, so I don't need tons of battery power time; 5-10 minutes would be plenty.

I was considering buying a Back-UPS ES, either a 550VA or a 650VA model, either of which appeared to meet my needs according to APC's online sizing tool.

But then I noticed that the 650VA model specs include a load capacity of 390W (and the 550VA model has a load capacity of 330W). Now I've just replaced that PCs OEM power supply with a nice sturdy 550W model, so I'm wondering whether attaching it to a UPS with just a 390W capacity is asking for trouble.

I know that the power supply will generally not draw its max power, but I am confused that PSU rating is not given as a factor in sizing a UPS. Or perhaps I am misunderstanding the "load capacity" spec.

Can anyone help me with this?

Thanks,

Jeremy

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:57 PM . Last Modified: ‎2024-03-26 12:53 AM

0 Likes
0
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:57 PM . Last Modified: ‎2024-03-26 12:53 AM

TheBackup wrote:
In order to realize the full capability of your PC's power supply you would have to be running multiple hard drives, high end processing, etc.

I'm not sure what the main use of the computer is, but if you find yourself utilizing high resource applications then in order to be safe you might want to go for a slightly larger unit.

Even though your computer has the 550W power supply you won't be pulling any more wattage than you were with the last power supply unless you increase the equipment inside the case.
While I do plan to install a bit of extra hardware, I do not expect to reach the new 550W limit. But I was advised that the cheap OEM 300W PSU that came with my PC might be a bit underpowered if I were to install stuff like a video card (it's currently using integrated video). So I decided to find a good deal on a PSU in the 500W range, which is by no means huge for mid-level PCs.


TheBackup wrote:
Hope this helps you out. If you want to get a definite answer the best thing would be to hook a kill-a-watt type meter up to the input on the PC power supply and find out what the PC draws when your running a resource heavy application.
Right. I guess what I was hoping to learn from this forum was how closely you need to pay attention to PSU capacity when sizing a UPS. In other words, is it considered bad practice to buy a UPS with a max output of less than your PSU's rating, or do you ignore the PSU rating and instead pay attention just to the power-consuming components inside the PC?

For the record, the PC is a PowerSpec B645, the specs for which are online here: <>. Core2 Duo CPU, 2 GB RAM, 2 SATA hard drives, and one IDE optical drive for now. I'll be adding a floppy drive and a second optical drive right away, and may or may not eventually replace the integrated video and sound.

The only other items that I expect to plug into the UPS would be my 20" LCD monitor and maybe my desk telephone.

Thanks for all assistance,

Jeremy

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:57 PM . Last Modified: ‎2024-03-26 12:53 AM

0 Likes
0
851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:57 PM . Last Modified: ‎2024-03-26 12:53 AM

Jeremy,

In order to realize the full capability of your PC's power supply you would have to be running multiple hard drives, high end processing, etc.

I'm not sure what the main use of the computer is, but if you find yourself utilizing high resource applications then in order to be safe you might want to go for a slightly larger unit.

Even though your computer has the 550W power supply you won't be pulling any more wattage than you were with the last power supply unless you increase the equipment inside the case.

Hope this helps you out. If you want to get a definite answer the best thing would be to hook a kill-a-watt type meter up to the input on the PC power supply and find out what the PC draws when your running a resource heavy application.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:57 PM . Last Modified: ‎2024-03-26 12:53 AM

0 Likes
0
851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:57 PM . Last Modified: ‎2024-03-26 12:53 AM

TheBackup wrote:
In order to realize the full capability of your PC's power supply you would have to be running multiple hard drives, high end processing, etc.

I'm not sure what the main use of the computer is, but if you find yourself utilizing high resource applications then in order to be safe you might want to go for a slightly larger unit.

Even though your computer has the 550W power supply you won't be pulling any more wattage than you were with the last power supply unless you increase the equipment inside the case.
While I do plan to install a bit of extra hardware, I do not expect to reach the new 550W limit. But I was advised that the cheap OEM 300W PSU that came with my PC might be a bit underpowered if I were to install stuff like a video card (it's currently using integrated video). So I decided to find a good deal on a PSU in the 500W range, which is by no means huge for mid-level PCs.


TheBackup wrote:
Hope this helps you out. If you want to get a definite answer the best thing would be to hook a kill-a-watt type meter up to the input on the PC power supply and find out what the PC draws when your running a resource heavy application.
Right. I guess what I was hoping to learn from this forum was how closely you need to pay attention to PSU capacity when sizing a UPS. In other words, is it considered bad practice to buy a UPS with a max output of less than your PSU's rating, or do you ignore the PSU rating and instead pay attention just to the power-consuming components inside the PC?

For the record, the PC is a PowerSpec B645, the specs for which are online here: <>. Core2 Duo CPU, 2 GB RAM, 2 SATA hard drives, and one IDE optical drive for now. I'll be adding a floppy drive and a second optical drive right away, and may or may not eventually replace the integrated video and sound.

The only other items that I expect to plug into the UPS would be my 20" LCD monitor and maybe my desk telephone.

Thanks for all assistance,

Jeremy

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore