Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Posted: 2021-06-29 11:04 PM . Last Modified: 2024-03-20 12:55 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:04 PM . Last Modified: 2024-03-20 12:55 AM
Hi,
We are an electronics workshop. One item the we use in-house is an APC SUA5000RMI5U UPS. Very handy peice of longtime reliable equipment.
Briefly, the existing 2x48vdc RBC battery packs are dead. However, we do have a 48vdc/1000Ah battery bank sitting here and would like to use that instead. Don't worry, we know precisely what we are doing.
One thing, the battery bank has it's own battery management controller so we would like to disable the UPS's on-board battery charging circuit in the most elegant way possible.
Any ideas? Firmware, config, hotkeys, schematic etc.
You assistance is greatly appreciated.
Regards,
Psyfy
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:04 PM . Last Modified: 2024-03-20 12:55 AM
As much as possible we recommend using APC batteries which has been tested to conform with the standards set by APC. To the best of my knowledge, there's no way for you to disable the battery charging circuit of our UPS.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:04 PM . Last Modified: 2024-03-20 12:55 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:04 PM . Last Modified: 2024-03-20 12:55 AM
Ineverdo anything like that, butdo not knowthe changes...might bebetterwith thetypeyou useUPSXL(can useexternalbattery /addlargerAh) stillhave to usethe settingofeeproom.
I'vegot aschematicSUA5000RMI5U,butstillonlyentitled toAPC
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:04 PM . Last Modified: 2024-03-20 12:55 AM
As much as possible we recommend using APC batteries which has been tested to conform with the standards set by APC. To the best of my knowledge, there's no way for you to disable the battery charging circuit of our UPS.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.