Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82506members
350107posts

SUA1500 having some issue, battery load bar drop suddenly

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
blackAces_apc
Commander
Commander
0 Likes
2
89

SUA1500 having some issue, battery load bar drop suddenly

This was originally posted on APC forums on 10/9/2009


Hi All

Guys need your help me again on my ups I have some issue on SUA15000I, S/N: AS0151131023 i think its a calibration or setting, after we replace the battery its show only 2 bars on the battery load side, i let the ups charge over night and its show a fully charge. I try to unplug the main supply and the UPS operate on battery then i plug back in the supply very thing is working fine, and then i try to unplug again the main supply but the battery was drop to 1 bar and the LEd is blinking w/ beeping..., Do i know what is wrong w/ our ups? or do i need any further test.. BTW, no load is connected w/ the upe during the test i done.


Accepted Solutions
blackAces_apc
Commander
Commander
0 Likes
0
89

Re: SUA1500 having some issue, battery load bar drop suddenly

This was originally posted on APC forums on 10/16/2009


Hi Bala

Thanks for the info, im not able to use the software to perform the runtime calibraton because i don't have the PCBE, so what i did was i let the ups run on battery, until its off, then i charge it again., so far quit ok already..

See Answer In Context

2 Replies 2
Techie_apc
Admiral
Admiral
0 Likes
0
89

Re: SUA1500 having some issue, battery load bar drop suddenly

This was originally posted on APC forums on 10/9/2009


Hanz,

Perform a manual runtime calibration to resolve this issue. You can find the manual runtime calibration instructions here. In case if the manual runtime calibration does not correct the situation, you may need to call in the regional Customer Care Center for the instructions on how to adjust the battery constant in the UPS through hyper terminal by using the serial cable that came with the UPS.

I hope that this helps.

blackAces_apc
Commander
Commander
0 Likes
0
90

Re: SUA1500 having some issue, battery load bar drop suddenly

This was originally posted on APC forums on 10/16/2009


Hi Bala

Thanks for the info, im not able to use the software to perform the runtime calibraton because i don't have the PCBE, so what i did was i let the ups run on battery, until its off, then i charge it again., so far quit ok already..