SRC1KUXI suddenly trips sometimes

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • SRC1KUXI suddenly trips sometimes
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
rajil.s_apc
Crewman rajil.s_apc
Crewman

Posted: ‎2022-04-30 11:37 AM . Last Modified: ‎2022-04-30 11:43 AM

0 Likes
1
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-30 11:37 AM . Last Modified: ‎2022-04-30 11:43 AM

SRC1KUXI suddenly trips sometimes

Hello,

 

I have a SRC1KUXI 800W online UPS. It has recently started tripping off when main goes off. I have checked the two SMF batteries attached and they showed 13.20V and 13.23V respectively. A self-test on the UPS comes out ok.

 

Here is a video after it has tripped,

https://i.imgur.com/4t4AaDS.mp4

 

The host is running apcupsd. This is what i get from a running system,

 

 

 

 

 

 

$apcaccess
APC      : 001,038,0930
DATE     : 2022-04-30 23:56:31 +0530  
HOSTNAME : nas
VERSION  : 3.14.14 (31 May 2016) unknown
UPSNAME  : pfsense
CABLE    : Ethernet Link
DRIVER   : NETWORK UPS Driver
UPSMODE  : Stand Alone
STARTTIME: 2022-04-30 23:27:28 +0530  
MASTERUPD: 2022-04-30 23:56:31 +0530  
MASTER   : x.x.x.x:3551
MODEL    : SRC1KUXI
STATUS   : ONLINE
LINEV    : 236.1 Volts
LOADPCT  : 55.0 Percent
BCHARGE  : 95.0 Percent
TIMELEFT : 175.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME  : 0 Seconds
OUTPUTV  : 236.2 Volts
LOTRANS  : 160.0 Volts
HITRANS  : 265.0 Volts
RETPCT   : 60.0 Percent
ITEMP    : 40.0 C
BATTV    : 28.8 Volts
LINEFREQ : 50.0 Hz
LASTXFER : Automatic or explicit self test
NUMXFERS : 0
TONBATT  : 0 Seconds
CUMONBATT: 0 Seconds
XOFFBATT : N/A
SELFTEST : NO
STATFLAG : 0x05000408
BATTDATE : 2018-09-19
NOMOUTV  : 230 Volts
NOMBATTV : 24.0 Volts
END APC  : 2022-04-30 23:57:27 +0530  

 

 

 

 

The UPS is only loaded 55%. Any idea what could be the issue?

 

Thanks

 

Attachments
Labels
  • Labels:
  • Home & Office - Universal Transfer
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-08-26 02:54 AM

0 Likes
0
1254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-26 02:54 AM

Hi @rajil.s_apc 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query.  Apologies for the late revert on this post of yours.

 

If you are still experiencing this issue with your UPS, may I know if we can remove the load attached to the UPS and then unplug the unit from the power source?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore