Posted: 2024-08-10 10:48 PM
SMT1500 with new battery
no power connected
UPS will turn on with batteries but as soon as you set the outputs to on UPS goes off
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-12 04:27 AM . Last Modified: 2024-08-12 06:41 AM
What are the active faults / error codes displayed by the UPS?!? If you have APC PCBE software installed what does the logs indicate?!?
Lastly, what is attached and their load on the unit?? What happens when there is no load attached and AC Mains is attached with the outputs turned on?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-12 08:26 PM
as it happens, removed the PCB so that I could remove & test the 2700uF cap = good, put it all back together, initially it was still faulting.
no load, only on battery, switch on UPS "output off" -> selected "on with no delay" and it would trip immediately.
now after a few failed attempts it is working without issue? has me stumped, left it overnight and UPS is relative cold say 16 deg C
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-13 02:50 AM
What are the answers to the questions I posed??
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-13 10:18 PM
What are the active faults / error codes displayed by the UPS - no error codes seen & nothing in the onboard logs
If you have APC PCBE software installed what does the logs indicate - not yet
Lastly, what is attached and their load on the unit - no load what so ever
What happens when there is no load attached and AC Mains is attached with the outputs turned on - worked without issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-14 05:59 AM
Guess what it is faulting again.
Ac mains works fine, turn ac off & ups immediately goes off completely.
could one of the changeover relays have stuck contacts?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-14 08:09 AM . Last Modified: 2024-08-14 08:11 AM
Let’s keep this simple what is the history of this UPS? Bought new? How long has it been in your service? What is the serial number of your unit?
What kind of communication do you have connected to the system? USB / RJ50 Serial? Smart Slot (NMC)? Smart Connect Cloud Portal Service?
If you have any of these in place upload the event / data logs. If you have nothing at all what does the on board logs say??
If there was a relay weld issue it typically would be declared.
Perform this simple test twice after completing the following: Brain Dead
Brain Dead: Disconnect all connected loads. Remove AC Mains from the wall outlet. Disconnect the battery cartridge. Press and hold the power button until you hear a click / beep.
Apply AC Mains to the system. Power on the unit. Toggle the outputs from on-off-on. Do this three times and report back what you see and observe.
If everything is working properly you should hear the internal relays clicking open / closed.
If everything is fine after doing the above. Reconnect the battery cartridge via the Anderson connector.
While the output is (On) what happens once you connect the battery cartridge??
Keep in mind at no time should there be ANY connected loads attached on the back during this test.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-16 05:55 PM
I have finally resolved the issue, was a bad connection/crip inside the anderson plus - replaced and no issue for 4 days so far
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-19 05:37 AM
That's great to hear and appreciate the follow up. If anything should change please do let me know.
Cheers! 👍