Replace Battery Signal Too Soon?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Replace Battery Signal Too Soon?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

0 Likes
2
767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

Replace Battery Signal Too Soon?

Previous APC models I have used at work that have tandem batteries, such as the the Back-UPS Pro 1000, would almost always die because one of the two batteries developed a short. Over the last weekend I had three Back-UPS RS 1200 models turn on the Replace Battery light, and in these instances both batteries test good, although obviously not as strong as when they were new. Is it just me or is the RS 1200 being more conservative in deciding when it needs new batteries? The net result will be buying more batteries ...

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • back-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

0 Likes
0
767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

The batteries don't necessarily have to be completely dead/damaged etc to fail a self test(which causes the replace battery led). The UPS does a self test every 2 weeks by default which checks multiple things such as discharge rate.. If the self test fails due to this or similar, you will not necessarily see that when testing the voltage, fuses, short etc. If you think the battery should be OK(due to age etc), you can initiate another self test to see if is passes.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

0 Likes
0
767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

all of the UPSs compare the voltage drop while on battery to a chart that it has within its firmware. if it is out of that range, then a replace battery indicator is signaled.

how old are these UPSs and batteries? where are they located? keep in mind environmental factors can affect battery lifetime. also, if the unit was bought after sitting for a year or so at a retailer, it can appear they are brand new but the batteries were sitting in storage.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

0 Likes
0
768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

The batteries don't necessarily have to be completely dead/damaged etc to fail a self test(which causes the replace battery led). The UPS does a self test every 2 weeks by default which checks multiple things such as discharge rate.. If the self test fails due to this or similar, you will not necessarily see that when testing the voltage, fuses, short etc. If you think the battery should be OK(due to age etc), you can initiate another self test to see if is passes.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore