Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82120members
349628posts

Replace Battery Signal Too Soon?

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
onegordo_apc
Cadet
0 Likes
2
87

Replace Battery Signal Too Soon?

This was originally posted on APC forums on 11/21/2011


Previous APC models I have used at work that have tandem batteries, such as the the Back-UPS Pro 1000, would almost always die because one of the two batteries developed a short. Over the last weekend I had three Back-UPS RS 1200 models turn on the Replace Battery light, and in these instances both batteries test good, although obviously not as strong as when they were new. Is it just me or is the RS 1200 being more conservative in deciding when it needs new batteries? The net result will be buying more batteries ...

Tags (1)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
87

Re: Replace Battery Signal Too Soon?

This reply was originally posted by Chris on APC forums on 11/22/2011


The batteries don't necessarily have to be completely dead/damaged etc to fail a self test(which causes the replace battery led). The UPS does a self test every 2 weeks by default which checks multiple things such as discharge rate.. If the self test fails due to this or similar, you will not necessarily see that when testing the voltage, fuses, short etc. If you think the battery should be OK(due to age etc), you can initiate another self test to see if is passes.

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
87

Re: Replace Battery Signal Too Soon?

This reply was originally posted by Angela on APC forums on 11/22/2011


all of the UPSs compare the voltage drop while on battery to a chart that it has within its firmware. if it is out of that range, then a replace battery indicator is signaled.

how old are these UPSs and batteries? where are they located? keep in mind environmental factors can affect battery lifetime. also, if the unit was bought after sitting for a year or so at a retailer, it can appear they are brand new but the batteries were sitting in storage.

BillP
Administrator Administrator
Administrator
0 Likes
0
88

Re: Replace Battery Signal Too Soon?

This reply was originally posted by Chris on APC forums on 11/22/2011


The batteries don't necessarily have to be completely dead/damaged etc to fail a self test(which causes the replace battery led). The UPS does a self test every 2 weeks by default which checks multiple things such as discharge rate.. If the self test fails due to this or similar, you will not necessarily see that when testing the voltage, fuses, short etc. If you think the battery should be OK(due to age etc), you can initiate another self test to see if is passes.