Recording mains supply conditions

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Recording mains supply conditions
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:35 AM

0 Likes
10
1686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:35 AM

Recording mains supply conditions

I need a unit that will record mains supply condition in a log so that I can inspect for outage time and duration up to a week past. Ideally this would be stand-alone, rather than require a computer. Ca anyone suggest which APC units to consider? Initial browsing has found no mention of this feature. Thanks

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:34 AM

0 Likes
0
1685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:34 AM

Thanks. Is there a UPS model that itself logs when it goes on battery?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:35 AM

0 Likes
0
1685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:35 AM

The power-chute bushiness edition software will log all voltages at a given interval you can set it to however many minutes, your best bet would be a Smart-Ups if you are wanting a ups you just said unit, also you would need a computer for powerchute

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:35 AM

0 Likes
0
1686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:35 AM

Thanks. Is there any unit that will log voltages without requiring a PC?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:35 AM

0 Likes
0
1685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:35 AM

You can buy a [network management card (NMC)|http://www.apc.com/products/family/?id=98] for SmartUPS UPSes. The NMC's event log records when the UPS goes on battery due to power outages and other line problems. It also has a data log that records voltages at a set interval, including the min and max voltage. The minimum interval is 1 minute.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:35 AM

0 Likes
0
1686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:35 AM

the new SMT or SMX line of single phase Smart UPS has an LCD menu on the front which is also able to keep the last 5 (or 10) transfer reasons in an event log of sorts as far as I know. Then, once you get to the larger UPSs like a Symmetra LX, they also have a PowerView LCD which records the last 64 events.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:35 AM

0 Likes
0
1686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:35 AM

delet comment

Message was edited by: Wwallender

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:34 AM

0 Likes
0
1686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:34 AM

the new SMT or SMX line of single phase Smart UPS has an LCD menu on the front which is also able to keep the last 5 (or 10) transfer reasons in an event log of sorts as far as I know.
Thanks. I've been unable to find such a model in the catalogue. e.g. the APC Smart-UPS 750VA LCD 230V (part number SMT750I) [Operation Manual|http://www.apcmedia.com/salestools/SCON-7NBSEM_R3_EN.pdfdocu] shows only a record of Last Transfer, which I take to refer to only one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:34 AM

0 Likes
0
1686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:34 AM

Thanks.

I'd investigate whether other vendors have a solution that better fits your needs, since a UPS is intended to be a UPS.
I have investigated, but have found nothing but very expensive mains supply analysers. If anyone can suggest a non-UPS supply monitor and logger, please do.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:34 AM

0 Likes
0
1686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:34 AM

While the SMT or SMX units will show the last several transfer events in the log, it doesn't show their times which you need in order to determine duration. So I think a UPS with an NMC is your best bet for a standalone unit from APC. I'd investigate whether other vendors have a solution that better fits your needs, since a UPS is intended to be a UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:34 AM

0 Likes
0
1686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:34 AM

i have an SMX1000 at my desk and it shows the last 10. i double checked with someone else and SMT750I will show the last 10 transfer reasons as well. you just need to make sure your LCD is in "advanced" menu mode so that you can access the logs functionality.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:34 AM

0 Likes
0
1686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:30 PM . Last Modified: ‎2024-03-20 02:34 AM

Thanks. Is there a UPS model that itself logs when it goes on battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore