RS900 Repeats Self-Test & USB connection broken

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • RS900 Repeats Self-Test & USB connection broken
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:23 AM . Last Modified: ‎2024-03-22 12:50 AM

0 Likes
1
860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:23 AM . Last Modified: ‎2024-03-22 12:50 AM

RS900 Repeats Self-Test & USB connection broken

I have two issues with my RS900. (Which I bought as a refurb 2 yrs ago and recently--i.e. 3 months--replaced both batteries.)

(1) Since I purchased the unit, the port (similar to an RJ45) into which the USB cable for the PC plugs in has not worked. I have multiple APC units and tried swapping different cables. My PC never recognized the unit. I called tech support and they told me they could not help me until I had the software installed. I could not install the software b/c the install program could not find an APC unit connected to my computer. Endless loop. I gave up on tech support/warranty and decided to live with not being able to control the unit from the PC.

(2) In the last week, my unit has begun repeating the self-test cycle every few minutes. This is on a PC that the rest of my family uses, so I have not determined how frequently it is occurring. So far, it seems that it starts about mid-day and repeats every 2-3 minutes for about 15-20 minutes. This repeating cycle is new....it used to just do the self-test once a day (as far as I can recall).

Any tips/suggestions on addressing these issues?
Are normal?

Thanks.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apc
  • back-ups
  • software
  • usb
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:23 AM . Last Modified: ‎2024-03-22 12:50 AM

0 Likes
0
860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:23 AM . Last Modified: ‎2024-03-22 12:50 AM

1.) when you say the port isnt working - how do you know? do you get an "unknown device" in the device manager (assuming this is Windows)? what are the symptoms of it not working. generally, we should be able to help you if you don't want to use the software..any more details on what you have tried so far would be helpful.

2.) just to be clear, during a self test, the online LED flashes (i think) and the on battery LED will be solid. the UPS would be operating on battery for 15-20 seconds and then going back online (solid green online LED only). is this whats happening? if not, please describe what is happening. are there any strange cables connected or anything new in this set up that you added?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:23 AM . Last Modified: ‎2024-03-22 12:50 AM

0 Likes
0
861
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:23 AM . Last Modified: ‎2024-03-22 12:50 AM

1.) when you say the port isnt working - how do you know? do you get an "unknown device" in the device manager (assuming this is Windows)? what are the symptoms of it not working. generally, we should be able to help you if you don't want to use the software..any more details on what you have tried so far would be helpful.

2.) just to be clear, during a self test, the online LED flashes (i think) and the on battery LED will be solid. the UPS would be operating on battery for 15-20 seconds and then going back online (solid green online LED only). is this whats happening? if not, please describe what is happening. are there any strange cables connected or anything new in this set up that you added?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore