RS 800 showing overload during a power fluctuation.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • RS 800 showing overload during a power fluctuation.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-11 10:53 PM . Last Modified: ‎2024-03-19 11:49 PM

0 Likes
4
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:53 PM . Last Modified: ‎2024-03-19 11:49 PM

RS 800 showing overload during a power fluctuation.

I have an RS 800 that signaled an overload and abruptly shut down my pc during a power fluctuation. There wasn't a power outage because everything such tvs, clocks and an unprotected pc stayed on. Lights flickered.  I reset the RS 800, turned the pc back on then unplugged the apc unit from the wall and it functioned properly. The building wiring fault indicator on the back is not on. I have several other different model units in my home that did not exhibit the same issue. The other models are an ES 550, ES 650, ES 750, and a RS 1200.  The attached load is 210 watts measured using a killawatt meter. The battery is six weeks old(since I installed the new battery pack). The estimated runtime seems correct and it passes the self test. Any ideas what caused this? It's something I can't replicate since pulling the plug didn't result in anything negative. I did lose faith in its ability to work as it should though and it will probably be relieved of its duties. Just realized this is likely the wrong area to post this...My bad.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • overload
  • rs800
  • shutdown
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-11 10:53 PM . Last Modified: ‎2024-03-19 11:49 PM

0 Likes
0
1300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:53 PM . Last Modified: ‎2024-03-19 11:49 PM

Jordan,                                                                                                                                                                                                                                                                                                                                                                    The light load(25 watts) that was setting off the overload originally was on the battery. I could replicate those results so I replaced the battery pack. I went ahead and followed the steps you suggested. Everything seems to work fine right now.  Thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-11 10:53 PM . Last Modified: ‎2024-03-19 11:49 PM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:53 PM . Last Modified: ‎2024-03-19 11:49 PM

Mike,

The watt capacity on the RS800 is 540w so crossing that threshold can cause an overload shutdown like you explained.  I know you mentioned your load is 210w, but is it possible you had anything else plugged in at that time or had equipment drawing more power than normal for more tasking processing?  All other indications you have given appear to indicate a healthy unit besides this issue.  Are you using any PowerChute software with this unit?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-11 10:53 PM . Last Modified: ‎2024-03-19 11:49 PM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:53 PM . Last Modified: ‎2024-03-19 11:49 PM

Jordan,

  During the initial incident the load on the ups was fairly light(web surfing). I did perform an additional test today by unplugging the ups unit with the cpu and graphics card loaded(365 watts) and experienced no issues. I'm currently not using the Powerchute software with that unit. The reasoning for replacing the batteries several weeks ago was because I would get an overload with as little as 25 watts. The RS 800 was primarily used to keep a modem, router and voip adapter powered during power interuptions. After replacing the battery pack I decided to use it to backup a pc and monitor since it was well within its power load range and use one of my smaller ups units for the low power devices (modem, router, etc.). I had an RS 1200 dedicated to that system (pc and monitor) originally but moved it to another location. The RS 800 seems to be working as it should so maybe it was just startled by its first test on a real load.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-11 10:53 PM . Last Modified: ‎2024-03-19 11:49 PM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:53 PM . Last Modified: ‎2024-03-19 11:49 PM

Hi Mike,

Interesting that this happened before with an even lighter load.  The battery health should not have a direct impact with an overload shutdown (unless it occured when the unit was on battery).  I am glad the unit is running fine now, but as a further precaution, I would run what is called a braindead procedure during downtime.

1)Turn the unit off

2)Unplug any equipment attached to the unit and unplug the unit itself from utility

3)Disconnect the internal battery

4)Hold the power button the unit for 20 solid seconds

5)Reconnect everything and boot up the unit

Sometimes the braindead can reset the intelligence and fix erroneous issues like you saw and sometimes it will bring to light an actual fault.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-11 10:53 PM . Last Modified: ‎2024-03-19 11:49 PM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:53 PM . Last Modified: ‎2024-03-19 11:49 PM

Jordan,                                                                                                                                                                                                                                                                                                                                                                    The light load(25 watts) that was setting off the overload originally was on the battery. I could replicate those results so I replaced the battery pack. I went ahead and followed the steps you suggested. Everything seems to work fine right now.  Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore