RS 1200 Running in Battery Mode Only

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • RS 1200 Running in Battery Mode Only
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 06:19 AM . Last Modified: β€Ž2024-03-21 05:37 AM

0 Likes
3
2360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 06:19 AM . Last Modified: β€Ž2024-03-21 05:37 AM

RS 1200 Running in Battery Mode Only

We have 3 RS 1200 units, two are working fine. Batteries were replaced in all 3 in fall 2010.

Today, the third unit switched to battery power and ran until battery ran out. It emitted 4 beeps every 30 seconds. The "Replace Battery" light is NOT on.

Technical information on the problem unit (according to PowerChute):

Model: Back-UPS RS 1200
Serial Number: JB0618020782
Firmware: 8.g1. D

We have tried plugging the unit into multiple AC jacks in multiple rooms, that are known to have good AC power. This does not help, the unit always run in battery-power mode.

I downloaded and installed PowerChute Personal Edition for Windows XP. After installation, first run of this program claimed that the battery "is more than 3 years old". This is not true, the battery was replaced last fall.

PowerChute:

- "Run Self Test" option: reports "Cannot complete self-test as there is no battery backup connected"
- "Voltage" page: UPS is set to intervene if voltage goes over 132 volts, or under 97 volts. "The current voltage" is shown varying between 91 and 96 volts. Although we don't have a voltmeter to check, there's no way the wall AC voltage is actually that low
- "Current Status" page: agrees that input voltage is in the low 90s

What is the most likely cause of this error? Could it be caused by a bad battery pack, or is it likely that some other part of the UPS has failed? Any ideas or comments appreciated.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 06:19 AM . Last Modified: β€Ž2024-03-21 05:37 AM

0 Likes
0
2360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 06:19 AM . Last Modified: β€Ž2024-03-21 05:37 AM

Good day Al,

If you do have a domestic UPS model that runs on 120V AC and was previously working and all of a sudden it stopped, most likely that one of the components failed. As per your post, you made sure that the UPS has been tried on known good working outlets and I presumed that the other UPSs that you have there has been tried on the same outlets as well.

If the other UPSs are working fine and this particular UPS detects that there is around ~90V AC that is being fed to it, the voltage sensor could be damaged already. If let's say the UPS was reading around ~100V or higher, we could try changing the sensitivity and transfer voltages.

On PCPE, if I am not mistaken there is a battery icon that you can click and it will ask you if you would like to change the battery replacement date to the current system date of your PC.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 06:19 AM . Last Modified: β€Ž2024-03-21 05:37 AM

0 Likes
0
2361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 06:19 AM . Last Modified: β€Ž2024-03-21 05:37 AM

Good day Al,

If you do have a domestic UPS model that runs on 120V AC and was previously working and all of a sudden it stopped, most likely that one of the components failed. As per your post, you made sure that the UPS has been tried on known good working outlets and I presumed that the other UPSs that you have there has been tried on the same outlets as well.

If the other UPSs are working fine and this particular UPS detects that there is around ~90V AC that is being fed to it, the voltage sensor could be damaged already. If let's say the UPS was reading around ~100V or higher, we could try changing the sensitivity and transfer voltages.

On PCPE, if I am not mistaken there is a battery icon that you can click and it will ask you if you would like to change the battery replacement date to the current system date of your PC.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 06:19 AM . Last Modified: β€Ž2024-03-21 05:37 AM

0 Likes
0
2360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 06:19 AM . Last Modified: β€Ž2024-03-21 05:37 AM

Thanks for your comments. I've since confirmed that the input AC is close to 120V but that UPS reports in the low 90s, looks like its voltage sensor is not working properly.

Just for grins I removed the upper front panel and blew out the upper interior of the unit with a compressed gas duster. There wasn't much dust considering over 4 years' continuous use. That had no effect on the problem.

I think I have to disagree with your idea of playing with the unit's voltage sensitivity if it had happened to read ~100V. The whole reason to have a UPS is to improve reliability. Using settings like that to try to compensate for a wonky sensor would just come back to bite you, likely in the very near future.

So, off to get a new UPS πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 06:19 AM . Last Modified: β€Ž2024-03-21 05:37 AM

0 Likes
0
2360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 06:19 AM . Last Modified: β€Ž2024-03-21 05:37 AM

You are very much welcome and it is okay if you do not want to change the sensitivity. I've put it on my post thinking that there might be other posters who might be experiencing some power problems, this might help them.

If you are planning to get a new UPS, you can use this UPS and go after our TradeUPS program. Our TradeUPS program offers you new UPS models on a discounted price. To know more, feel free to call our APC Tech Support Hotline at 800-800-4272.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore