Protection from LIghtning - Back-UPS BR1000

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Protection from LIghtning - Back-UPS BR1000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:48 AM . Last Modified: ‎2024-03-26 03:58 AM

0 Likes
9
2469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:48 AM . Last Modified: ‎2024-03-26 03:58 AM

Protection from LIghtning - Back-UPS BR1000

Hello,

I use the APC BR 1000 Back-UPS.  I have my pc,  modem and router plugged into the slots for Battery Backup outlets with surge  protection. I am NOT using the In/Out Ethernet surge-protected ports on my BR 1000. Does this mean that the modem, router, pc are not protected from lightning strikes? I am concerned that a powerful lightning strike could send a surge thru the modem to the connected router and subsequently to my pc. I am obviously not an electrician embarassed

 

Thanks,

Bryan

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:57 AM

0 Likes
0
2468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:57 AM

Thank you very much Matt.  Your assistance is greatly appreciated.  H

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:48 AM . Last Modified: ‎2024-03-26 03:58 AM

0 Likes
0
2468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:48 AM . Last Modified: ‎2024-03-26 03:58 AM

Hi Howard

Yes it is quite possible that a lightning strike or any transients can be transmitted through the data lines coming into your equipment and potentially damage them.

It is always recommended to protect any power cables and data cables coming into the building before they connect to equipment.

We have a white paper on the subject if you'd like some bedtime reading!

https://www.apc.com/salestools/SADE-5TNRN6/SADE-5TNRN6_R1_EN.pdf

Regards

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:48 AM . Last Modified: ‎2024-03-26 03:58 AM

0 Likes
0
2468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:48 AM . Last Modified: ‎2024-03-26 03:58 AM

Hi Matt,

   Thank you for the information. Years ago my computer was severely damaged by a powerful lightening strike so I installed  a surge protection device which allowed me run the phone  line into the surge protector.  A few months later we had another powerful lightening strike which destroyed the surge protector  but did not harm any of my  devices. This type of surge protector is  mentioned in the article where the surge protector 'takes the hit' but spares the computer/equipment. My question is as follows: currently the  the modem connects to the router. If I disconnect the ethernet line  which currently runs from the modem to the router and instead run the same  line from the modem to the modem  (IN) slot in in the BR1000  Backup and then run a line from the PC (OUT) slot in the BR1000 to the router,will this protect my computer from lightening? If so will there be any degradation in my internet speed?

Thank you very much for your assistance,

Howard

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:58 AM

0 Likes
0
2468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:58 AM

Hi Howard

It would be better to run the from the wall socket of the incoming internet connection to the Back UPS and then from the Back UPS to the modem.

What kind of internet connection is coming into the building?

In terms of internet speed there is always some attenuation of the signal when more electronics is introduced, but in terms of speed, it depends on the strength of the original signal, our circuitry for dataline protection introduces less than 0.1db of signal loss.

Regards

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:58 AM

0 Likes
0
2468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:58 AM

Hi Matt,

   I will check when I get home tonight (I am in New Jersey) but I don't think the Optimum cable which enters our home will feed into the modem (IN) slot behind the BackUPS.  Thanks again.  Howard

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:58 AM

0 Likes
0
2468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:58 AM

Hi again  Matt,

    The cable which enters our home is an RG-11 line.

Thanks,

Howard

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:57 AM

0 Likes
0
2468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:57 AM

Hi Howard

Whilst the BR1000 data line protection ports are RJ45, they will accept and protect the RJ11.

Regards

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:57 AM

0 Likes
0
2468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:57 AM

Hi Matt,

    My incoming internet/phone cable is  actually a PPC EX6 coax cable.  So just to confirm I  am connecting my incoming internet/phone cable to the BR1000 coax(in) port and then using the coax cable which came with the BR1000 to connect from the BR1000 coax (out) back to the modem.  Correct?

Howard

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:57 AM

0 Likes
0
2468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:57 AM

Hi Howard

Yes that's correct.

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:57 AM

0 Likes
0
2469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:49 AM . Last Modified: ‎2024-03-26 03:57 AM

Thank you very much Matt.  Your assistance is greatly appreciated.  H

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore