Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Problems with Back UPS 1500VA

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Problems with Back UPS 1500VA
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
152
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:28 AM . Last Modified: ‎2024-03-22 01:28 AM

0 Likes
3
1855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:28 AM . Last Modified: ‎2024-03-22 01:28 AM

Problems with Back UPS 1500VA

Firstly, a few details:

Model: APC Back UPS RS 1500 (230V) / BR1500-IN
Purchased: on 5/5/10 in Bangalore, India
Serial #: JB********** (JB followed by 10 numbers)
QA Test:
-------Revision: 69.73.585.38.81
-------Date: 3/22/10
-------Every test says "PASSED" and at the bottom it says "Overall Passed!" and there's a stamp which reads "BATTERY OK". Has a signature too.
------

The problems:

*1. When the UPS is in battery mode, the PSU (not UPS) (Corsair TX650) makes a buzzing noise.*
------I have learnt that this is normal for a Back-UPS, but it is very annoying. Is there any way to get rid of the noise (like using a stabilizer)? If no, can I get a Smart-UPS of the same capacity in exchange for my Back-UPS (_the Smart-UPS should be expendable by adding a battery pack_)

*2. The speakers also make a similar noise when the UPS is in battery mode.*
------If I connect headphones to the speaker, the headphones start making noise and the speakers stop

*3. When there is no AC power, the UPS shuts down and flashes the overload indicator*
-----I tired everything I could think of, including removing every cable/cord connected to the UPS, but it still says overloaded when it performs a self test or does not receive AC power. This problem started just a few hours ago.

I would be very grateful if you can tell me how I can stop/prevent these problems.

PS: It is very frustrating to post here. My post always loses formatting.

The message is loosing formatting, re-posting now.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • back-ups
  • beeping
  • noise
  • overload
  • psu
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:28 AM . Last Modified: ‎2024-03-22 01:28 AM

0 Likes
0
1854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:28 AM . Last Modified: ‎2024-03-22 01:28 AM

Firstly, a few details:

Model: APC Back UPS RS 1500 (230V) / BR1500-IN
Purchased: on 5/5/10 in Bangalore, India
Serial #: JB********** (JB followed by 10 numbers)
QA Test:
-------Revision: 69.73.585.38.81
-------Date: 3/22/10
-------Every test says "PASSED" and at the bottom it says "Overall Passed!" and there's a stamp which reads "BATTERY OK". Has a signature too.
------

The problems:

*1. When the UPS is in battery mode, the PSU (not UPS) (Corsair TX650) makes a buzzing noise.*
------I have learnt that this is normal for a Back-UPS, but it is very annoying. Is there any way to get rid of the noise (like using a stabilizer)? If no, can I get a Smart-UPS of the same capacity in exchange for my Back-UPS (_the Smart-UPS should be expendable by adding a battery pack_)

*2. The speakers also make a similar noise when the UPS is in battery mode.*
------If I connect headphones to the speaker, the headphones start making noise and the speakers stop

*3. When there is no AC power, the UPS shuts down and flashes the overload indicator*
-----I tired everything I could think of, including removing every cable/cord connected to the UPS, but it still says overloaded when it performs a self test or does not receive AC power. This problem started just a few hours ago.

I would be very grateful if you can tell me how I can stop/prevent these problems.

PS: It is very frustrating to post here. My post always loses formatting.

The message is loosing formatting, re-posting now.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:28 AM . Last Modified: ‎2024-03-22 01:28 AM

0 Likes
0
1855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:28 AM . Last Modified: ‎2024-03-22 01:28 AM

I do have PowerChute installed (for now), and it says "your battery backup is currently supplying 112 watts of power". It sometimes increases to 150W, but I don't think it matters, as even if there are no equipments connected, it says overload.

And now I can see the "replace battery" indicator lit (it started 10 mins ago), and PowerChute also tells me I need to replace the battery. It's only been 10 days since I bought this UPS, is something wrong with the battery?

One last question: Is there a Smart UPS of 1500VA which can be extended by connecting an external battery pack? I couldn't find any in apc.com

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:28 AM . Last Modified: ‎2024-03-22 01:28 AM

0 Likes
0
1855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:28 AM . Last Modified: ‎2024-03-22 01:28 AM

Yes, I think something is wrong with the UPS and/or battery. I would suggest calling in to tech support since you said this was purchased recently. They should be able to help determine what's wrong with the UPS and issue a replacement part/unit if necessary.

Yes, the [SMX1500RM2U|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SMX1500RM2U] has to option to connect external battery packs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:28 AM . Last Modified: ‎2024-03-22 01:28 AM

0 Likes
0
1855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:28 AM . Last Modified: ‎2024-03-22 01:28 AM

Firstly, a few details:

Model: APC Back UPS RS 1500 (230V) / BR1500-IN
Purchased: on 5/5/10 in Bangalore, India
Serial #: JB********** (JB followed by 10 numbers)
QA Test:
-------Revision: 69.73.585.38.81
-------Date: 3/22/10
-------Every test says "PASSED" and at the bottom it says "Overall Passed!" and there's a stamp which reads "BATTERY OK". Has a signature too.
------

The problems:

*1. When the UPS is in battery mode, the PSU (not UPS) (Corsair TX650) makes a buzzing noise.*
------I have learnt that this is normal for a Back-UPS, but it is very annoying. Is there any way to get rid of the noise (like using a stabilizer)? If no, can I get a Smart-UPS of the same capacity in exchange for my Back-UPS (_the Smart-UPS should be expendable by adding a battery pack_)

*2. The speakers also make a similar noise when the UPS is in battery mode.*
------If I connect headphones to the speaker, the headphones start making noise and the speakers stop

*3. When there is no AC power, the UPS shuts down and flashes the overload indicator*
-----I tired everything I could think of, including removing every cable/cord connected to the UPS, but it still says overloaded when it performs a self test or does not receive AC power. This problem started just a few hours ago.

I would be very grateful if you can tell me how I can stop/prevent these problems.

PS: It is very frustrating to post here. My post always loses formatting.

The message is loosing formatting, re-posting now.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore