Problem with battery not charging on a XS1300LCD

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Problem with battery not charging on a XS1300LCD
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:36 AM . Last Modified: ‎2024-03-22 01:20 AM

0 Likes
8
1768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:36 AM . Last Modified: ‎2024-03-22 01:20 AM

Problem with battery not charging on a XS1300LCD

We had a power outage that completely drained the battery on the XS1300. Then, the power came back, the UPS got back online but the battery won't charge. The battery indicator is flashing as long as the UPS beeping every second or so. I checked the manual to see if it could be that the battery is at its end of life but the online battery bad indicator is not displayed. The word "LOW" is not displayed next to the battery charge. I couldn't find this specific condition described in the manual.

So, what could it be? The battery?

Thanks in advance!

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:37 AM . Last Modified: ‎2024-03-22 01:20 AM

0 Likes
0
1768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:37 AM . Last Modified: ‎2024-03-22 01:20 AM

We had a power outage that completely drained the battery on the XS1300. Then, the power came back, the UPS got back online but the battery won't charge. The battery indicator is flashing as long as the UPS beeping every second or so. I checked the manual to see if it could be that the battery is at its end of life but the online battery bad indicator is not displayed. The word "LOW" is not displayed next to the battery charge. I couldn't find this specific condition described in the manual.

So, what could it be? The battery?

Thanks in advance!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:36 AM . Last Modified: ‎2024-03-22 01:20 AM

0 Likes
0
1768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:36 AM . Last Modified: ‎2024-03-22 01:20 AM

I have been having the very same problem. Flashing battery indicator and all. The only power outage I know of was on 9/11, over a month ago. Why it's malfunctioning now, I don't know.

After viewing this thread, I called APC and spoke to "Ron." Moderately accented -- overseas tech support? I had to get down on hands and knees and physically get the numbers off the UPC label on the bottom of the unit (note: Why does APC put it in the most inconvenient and hard to get to spot?). The numbers were essentially identical to the numbers that displayed on the Powerchute software. So why did I have to get on my hands and knees? Still don't have an answer to that....

So then, I had to turn the unit over, remove the battery cover and visually confirm that the battery was connected. Probably necessary, but again, a pain in the neck.

So then, "Ron" offered to send a replacement battery. To which I replied, what if the unit itself is defective? I advised that, in this very thread, the user confirmed that APC had sent a new unit right away. He said he could do that, but I would have to pay shipping to return the defective unit. Given the weight, I said, "no way!" He put me on hold for about 5 minutes, came back and agreed to send me a whole new unit with a call tag for shipping return. 5-7 business days "lead time" which means I won't expect to see it for a couple of weeks minimum.

End result [so far]: I should be getting what I should have gotten in the first place. I had to be slightly unpleasant, though, and the whole experience was like having a root canal.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:36 AM . Last Modified: ‎2024-03-22 01:20 AM

0 Likes
0
1768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:36 AM . Last Modified: ‎2024-03-22 01:20 AM

Hi Laurent,

Can you provide the exact model and serial number of the UPS? These details can be found either at the back or bottom portion of the UPS we would need these numbers to properly troubleshoot the issue. Generally, if the UPS shows a flashing replace battery indicator it means that the battery is not connected/ detected. We would start with checking the battery connection and condition, try reseating the battery wires/ connector and you can also try unplugging the UPS from the power source and see if it will drop the load.

JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:36 AM . Last Modified: ‎2024-03-22 01:20 AM

0 Likes
0
1768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:36 AM . Last Modified: ‎2024-03-22 01:20 AM

Jon,

The serial number is 880750R17630 and the model is XS1300LCD.

I have tried to reseat the battery. Strange thing is that when I turn on the UPS, it seems to work for maybe 5 minutes. I see that the battery charge is about one quarter. Then, after about 5 minutes, it starts beeping and the battery charge indicator gets empty and starts flashing. No other indicator of a bad battery or any system fault appears. I did the test to connect one cell at a time to the UPS, just for a test. One of the cell does seem to register with the UPS who starts charging it while the other cell doesn't show up on the UPS, the UPS still thinks there is no battery connected. Is it possible that one of the cell has turned bad, which would prevent the UPS to report a bad battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:36 AM . Last Modified: ‎2024-03-22 01:20 AM

0 Likes
0
1768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:36 AM . Last Modified: ‎2024-03-22 01:20 AM

Laurent,

If you have another UPS of the same model you can also swap their batteries to see if it follows the unit or the battery. There's also a possibility on why did the UPS shows that it cannot detect the battery is due to a damage/ broken battery cell.

Our Back-UPS product line has a 3-year warranty on it, I suggest that you call the APC Support Team to check if the unit is within warranty and to further help you with the troubleshooting. You can reach them at 800.800.4272

JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:37 AM . Last Modified: ‎2024-03-22 01:20 AM

0 Likes
0
1768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:37 AM . Last Modified: ‎2024-03-22 01:20 AM

You're welcome Laurent, let us know about the outcome.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:37 AM . Last Modified: ‎2024-03-22 01:20 AM

0 Likes
0
1768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:37 AM . Last Modified: ‎2024-03-22 01:20 AM

Someone from the support team has already taken steps to ship me another unit. I had opened a support ticket parallel to this forum post. I'm really surprised and pleased at APC support. It's not very common these days to get that kind of support. I'm glad I did choose APC when I bought this UPS!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:37 AM . Last Modified: ‎2024-03-22 01:20 AM

0 Likes
0
1768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:37 AM . Last Modified: ‎2024-03-22 01:20 AM

Thanks Laurent. Let us know when you receive the replacement unit.

jonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:37 AM . Last Modified: ‎2024-03-22 01:20 AM

0 Likes
0
1769
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:37 AM . Last Modified: ‎2024-03-22 01:20 AM

We had a power outage that completely drained the battery on the XS1300. Then, the power came back, the UPS got back online but the battery won't charge. The battery indicator is flashing as long as the UPS beeping every second or so. I checked the manual to see if it could be that the battery is at its end of life but the online battery bad indicator is not displayed. The word "LOW" is not displayed next to the battery charge. I couldn't find this specific condition described in the manual.

So, what could it be? The battery?

Thanks in advance!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore