Pro 1500, new battery won't hold a charge

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Pro 1500, new battery won't hold a charge
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
125
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:29 AM . Last Modified: ‎2024-03-27 01:42 AM

0 Likes
3
1955
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:29 AM . Last Modified: ‎2024-03-27 01:42 AM

Pro 1500, new battery won't hold a charge

Hi everyone, I've been Googling and searching here and looking at videos but I'm not getting an answer.

My company uses a Pro 1500. The battery was starting to die after all these years so we ordered a new one. I installed it last Friday (it's the newer, super easy to install battery). I thought it would need a weekend to charge up, but yesterday, I saw that the battery is flashing. The icons say that it's online, there's zero load (I took everything off it with the hopes it'll charge). When I go through the screens, there's 0W load, 0% load, 120v out, 60hz out., 119v in, 0 events, and 0 mins run time. The change battery icon isn't flashing, no other icons are lit.

We're in a Mac environment so I can't use Powerchute, as well, there's no USB cable for it.

Before I send the battery back, is there anything I should try?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:29 AM . Last Modified: ‎2024-03-27 01:42 AM

0 Likes
0
1955
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:29 AM . Last Modified: ‎2024-03-27 01:42 AM

Yes. You can try resetting the unit.

Disconnect it from all sources of power, including the battery. Then depress the power button for a few seconds. Reconnect the battery and restore power to the unit.

I have had a unit or two where doing that proved not to be enough. In those cases, indicating to the unit that its battery had been replaced solved the problem. As far as I'm aware, you would require the USB communication cable in order to do this. Powerchute would be the easiest way if there are any PCs running Windows available, as it presents a "replace battery" button that updates a flag within the UPS itself. If not, I believe apcupsd can also make this change, and it is available for Macintosh systems.

There is a slight possibility that the UPS itself has suffered a failure of some kind.

Someone affiliated with APC or Schneider Electric may have other ideas. I'm basically just an end user and do not represent either company in any way.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:29 AM . Last Modified: ‎2024-03-27 01:42 AM

0 Likes
0
1955
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:29 AM . Last Modified: ‎2024-03-27 01:42 AM

Thanks, William

I just tried that and it's still the same.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:29 AM . Last Modified: ‎2024-03-27 01:42 AM

0 Likes
0
1955
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:29 AM . Last Modified: ‎2024-03-27 01:42 AM

Aron,

Reset the Back-UPS

1: Disconnect any attached load.

2: Unplug the UPS from the wall socket.

3: Disconnect the UPS' internal battery.

4: Push and hold the "On" button on the UPS for 5 seconds

5: Reconnect internal battery.

6: Plug UPS in to known good power source.

7: Turn UPS on.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:29 AM . Last Modified: ‎2024-03-27 01:42 AM

0 Likes
0
1956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:29 AM . Last Modified: ‎2024-03-27 01:42 AM

Yes. You can try resetting the unit.

Disconnect it from all sources of power, including the battery. Then depress the power button for a few seconds. Reconnect the battery and restore power to the unit.

I have had a unit or two where doing that proved not to be enough. In those cases, indicating to the unit that its battery had been replaced solved the problem. As far as I'm aware, you would require the USB communication cable in order to do this. Powerchute would be the easiest way if there are any PCs running Windows available, as it presents a "replace battery" button that updates a flag within the UPS itself. If not, I believe apcupsd can also make this change, and it is available for Macintosh systems.

There is a slight possibility that the UPS itself has suffered a failure of some kind.

Someone affiliated with APC or Schneider Electric may have other ideas. I'm basically just an end user and do not represent either company in any way.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:29 AM . Last Modified: ‎2024-03-27 01:42 AM

0 Likes
0
1956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:29 AM . Last Modified: ‎2024-03-27 01:42 AM

Thanks, William

I just tried that and it's still the same.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:29 AM . Last Modified: ‎2024-03-27 01:42 AM

0 Likes
0
1956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:29 AM . Last Modified: ‎2024-03-27 01:42 AM

Aron,

Reset the Back-UPS

1: Disconnect any attached load.

2: Unplug the UPS from the wall socket.

3: Disconnect the UPS' internal battery.

4: Push and hold the "On" button on the UPS for 5 seconds

5: Reconnect internal battery.

6: Plug UPS in to known good power source.

7: Turn UPS on.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore