Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Please select a country to continue with beta search.
Posted: 2021-06-29 06:53 PM . Last Modified: 2024-03-21 03:20 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:53 PM . Last Modified: 2024-03-21 03:20 AM
Will there be a powerchute for vista for other operating systems than english?
Or will the english os only program work on my finnish vista.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:54 PM . Last Modified: 2024-03-21 03:20 AM
PowerChute Personal Edition does support Japanese, Chinese, French, Russian
Polish, Hungarian, Italian, Spanish, Portuguese, German OS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:54 PM . Last Modified: 2024-03-21 03:20 AM
Hello Juhani,
Sorry for the delayed response. The only other version of PowerChute Personal Edition that is currently available besides English is Japanese.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:54 PM . Last Modified: 2024-03-21 03:20 AM
PowerChute Personal Edition does support Japanese, Chinese, French, Russian
Polish, Hungarian, Italian, Spanish, Portuguese, German OS.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.