Anyone know if you can use PowerChute to monitor two UPS at the same time?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:09 PM . Last Modified: 2024-03-21 03:12 AM
Do you mean can one machine monitor two different UPS's at once?
If so, no, it will only see one UPS.
However, if you have 2 machines, 2 UPS's, you can do a 1:1 physical connection and depending on the type of UPS (Mainly, Smart-UPS) you can use one machine to monitor both.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:09 PM . Last Modified: 2024-03-21 03:12 AM
Could you please clarify what kind of PowerChute software you are referring to?
PowerChute Network Shutdown can be set up to monitor the status of two like UPSs by performing a custom installation.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:09 PM . Last Modified: 2024-03-21 03:12 AM
Do you mean can one machine monitor two different UPS's at once?
If so, no, it will only see one UPS.
However, if you have 2 machines, 2 UPS's, you can do a 1:1 physical connection and depending on the type of UPS (Mainly, Smart-UPS) you can use one machine to monitor both.