Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

New UPS "BR900GI" suddenly runtime is very low

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • New UPS "BR900GI" suddenly runtime is very low
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
154
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:48 PM . Last Modified: ‎2024-03-20 03:48 AM

0 Likes
5
2038
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:48 PM . Last Modified: ‎2024-03-20 03:48 AM

New UPS "BR900GI" suddenly runtime is very low

Hello,

I have purchased new UPS 2 month ago Model : BR900GI, It was working very good and giving me around 45:50 minutes runtime at 86 watt load which is 20% of UPS load capacity

suddenly i found the runtime became 3 minutes at the same load and the same devices " My PC 70 watt, wireless router 8 watt, small speaker 8 watt "

is there any explanation for this problem ?

please help


Best Regards 

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • br900gi
  • low_battery_duration
  • runtime
  • very
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:48 AM

0 Likes
0
2038
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:48 AM

So when you let the UPS turn off with the 240 watt load, how long did it run? The 4 minutes? Or are you saying the 4 minutes was a second test with 86 watts?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:48 PM . Last Modified: ‎2024-03-20 03:48 AM

0 Likes
0
2038
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:48 PM . Last Modified: ‎2024-03-20 03:48 AM

The runtime reported while the UPS is online is a really good estimate. Sometimes this number can appear incorrect but the question will be, when the UPS goes to battery, what does the value change to? And if you remove AC power or unplug the UPS from the wall, does it really last 3 minutes or more like 45? If you do this, I'd use a non-critical load to test this and remove your computer and the USB cable to the UPS so that it does not interfere with an early shutdown. You'd ideally let the UPS run until it turns off and charge back up and see if any change. This could help tell if the problem is just a calibration or something has happened and the runtime is really around 3 minutes.

Have you had any recent power events/outages, is that when you noticed this value changed?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:48 AM

0 Likes
0
2038
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:48 AM

No, When i unattached USB cable and unplug UPS from AC utility it's really last for 3 minutes and turned off due to low battery

about battery calibration after the ups turned off should " i leave the same load attached while it charging" or  " unplug any load and leave it charge back with no load "

and is there any way to maintain the UPS processor through the usb cable because manual calibration is not easy .

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:48 AM

0 Likes
0
2038
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:48 AM

For these UPSs, unfortunately they don't really offer a quick calibration or a command like larger UPS units do. A manual calibration is the only way to do it. I would put about 30% or more load on there to make sure the calibration is worth while and make sure the load does not fluctuate. When you let it charge back up, you can do it either way. Just keep in mind if you turn on the UPS and you have a power event while it is charging, it will make the charging take longer overall. But, it is not a requirement and has no impact if you charge it while the UPS is on or off or what the load is when charging.

If it turns out to be the battery capacity, it sounds like it is in warranty so you'd be entitled to a battery I think, based on the purchase date.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:48 AM

0 Likes
0
2038
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:48 AM

I did battery calibration with load 53% " 2 light lamps each 100 watt and Laptop 40watt " = 240 watt total / 450 watt battery capacity,  and ups turned off then i left it charging with no load " 

in the morning i found the run time at load "86 watt" become 20 minutes instead of 4 minutes but when i unplug AC utility it's actually giving me 4 minutes before turned off

and there is something i noticed that last replacement battery date was a year earlier the time i purchased my UPS .

this mean the ups was in the store for 1 year before i purchased it .

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:48 AM

0 Likes
0
2039
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:48 AM

So when you let the UPS turn off with the 240 watt load, how long did it run? The 4 minutes? Or are you saying the 4 minutes was a second test with 86 watts?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore