New UPS clicking couple of times a week

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • New UPS clicking couple of times a week
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
6
741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

New UPS clicking couple of times a week

I have used a Back-UPS ES 500 for a number of years. I just upgraded to the BP700UC when I bought a new computer.

I have noticed that every once in a while I hear a click from the UPS (no beep), perhaps a couple of times a week. Today I heard the click (no beep) and a pop-up on my computer said the UPS was on battery power. My desk light was on. The menu bar icon displayed the charging symbol and showed 99% which went back to 100% in a minute and icon went to the on line symbol.

Any thoughts on what is happening? I never experienced this with the Back-UPS ES 500. Note, the load on the BP700UC is about 230 watts.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

Yeah, there are many possibilities, like the electric company using an automated meter reading system that communicates over the power lines, or an appliance kicking on mid-afternoon. Hopefully adjusting the sensitivity takes care of things.

Since you have a scope, you might try using a sine reference on one probe and the AC line on the other. Get them in phase, then trigger on the difference going above a certain amount.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

I have used a Back-UPS ES 500 for a number of years. I just upgraded to the BP700UC when I bought a new computer.

I have noticed that every once in a while I hear a click from the UPS (no beep), perhaps a couple of times a week. Today I heard the click (no beep) and a pop-up on my computer said the UPS was on battery power. My desk light was on. The menu bar icon displayed the charging symbol and showed 99% which went back to 100% in a minute and icon went to the on line symbol.

Any thoughts on what is happening? I never experienced this with the Back-UPS ES 500. Note, the load on the BP700UC is about 230 watts.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

Robert,

It appears that your UPS makes clicking sound whenever it transfers from online to on battery/on battery to online. The UPS will run on battery whenever UPS deems the power is unsafe for your computer equipment. I suggest you to adjust the UPS sensitivity to Low. This would allow the unit to be more tolerant of voltage distortion and, therefore, make less transfer to battery. Here are the steps to adjust the UPS sensitivity to Low.

Open the Power chute software>Configuration>Sensitivity

Once you inside Sensitivity, you will find the option to adjust the UPS sensitivity to Low.

I hope that this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

Techie wrote:
Open the Power chute software>Configuration>Sensitivity

Once you inside Sensitivity, you will find the option to adjust the UPS sensitivity to Low.
There is no such thing. I'm on OSX using the latest version of PC for Mac (1.3.4) and it's very basic. Note, I uninstalled it since the Pref Pane that is part of OSX 10.5 offers more options but not sensitivity.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

You are correct. Unfortunately, the UPS sensitivity can not be adjusted through MAC OS X.

In case if you/or any one of your friend has got a Windows OS system....

You can adjust the UPS sensitivity through Windows OS(XP, 2000, Vista, ME and 98) based Power Chute Personal Edition software.
http://www.apc.com/products/family/index.cfm?id=129&ISOCountryCode=US

You can connect the UPS to any one of the above Windows OS computer via the USB cable, and install the PCPE version 1.5, 2.0 or 2.2(view the compatible chart for more information).

You can reconnect the UPS to the MAC system after adjusting the UPS sensitivity. The Setting will not change until you make any changes through the PCPE software.

If you do not have the Windows OS system, then you may need to check the wall outlet to see if it provides good power to the UPS. As I said earlier, the UPS will run on battery if the input power is not normal in order to protect your connected equipment from power problems. The relay inside the UPS may be the root cause for the clicking sound. The relay activates when the UPS switches to battery/from battery to online. Is the clicking sound abnormally loud? Make sure that the UPS power cord is directly plugged into the wall outlet. Connect the UPS to any other working outlet and check if it makes difference.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

Friends don't use Windows πŸ˜‰

I guess that the original reason for my post was that in five years of operation, I never experienced this on my Back-UPS ES 500 so was somewhat surprised to see it on the BP700UC.

With regard to the power it is clean, looked at it with a scope, and exactly 120 volts. UPS plugged directly into the outlet.

This seems to happen only mid afternoon. The power company may be switching things to maintain proper load factor causing small glitches on the line. Strange though that my cheapest and most sensitive digital clock doesn't see it and start blinking.

My son has a Win laptop; also uses an APC UPS with his Win desktop. I excuse him though since he was smart enough to stay with XP and uses Firefox πŸ˜‰ Next time he visits I'll have him check the sensitivity setting.

Thanks for your information.

Message was edited by: bobsenior

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

Yeah, there are many possibilities, like the electric company using an automated meter reading system that communicates over the power lines, or an appliance kicking on mid-afternoon. Hopefully adjusting the sensitivity takes care of things.

Since you have a scope, you might try using a sine reference on one probe and the AC line on the other. Get them in phase, then trigger on the difference going above a certain amount.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of