Monitor (2) Backups RS 1500 on same machine?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Monitor (2) Backups RS 1500 on same machine?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
116
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:46 AM . Last Modified: ‎2024-03-27 02:09 AM

0 Likes
5
1339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:46 AM . Last Modified: ‎2024-03-27 02:09 AM

Monitor (2) Backups RS 1500 on same machine?

I Have a large rackmount server that controls the automation, AV, etc for my entire house. I have a true, redundant power supply with (2) power cords feeding into the server. I have (2) APC Backups RS 1500 (each with the BR24BP) and a copy of Powerchute Personal Edition instilled on the server. Is there any way to get PE to monitor 2 devices, or is there a business addition of the Powerchute software that supports my devices?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:47 AM . Last Modified: ‎2024-03-27 02:09 AM

0 Likes
0
1338
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:47 AM . Last Modified: ‎2024-03-27 02:09 AM

I have it configured for USB, along with all the other recommended settings for USB type in the configuration file but no dice. The latest versions are preconfigured for USB devices anyways, but I verified everything matched the instructions none the less. I'm not 100% on the driver. I see the driver.ini file and I installed it. I can either of the UPS's to show up in device manager under BOTH batteries AND HID dvices, but still no communication. I manually specified the driver as instructed, and when it finishes, device manager shows a driver date of 2006/Microsoft. I have repeated this process many times,using every trickI can think of with the same results. I've uninstalled and reinstalled APCUPSD, restarted the server, etc. When I run the APCTEST utility (with APCUPSD services stopped) it always comes back with a fatal error during port configuration at line 321.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:46 AM . Last Modified: ‎2024-03-27 02:09 AM

0 Likes
0
1338
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:46 AM . Last Modified: ‎2024-03-27 02:09 AM

Hi,

With Back-UPS and PowerChute you can only be monitored by 1 system at a time. With Smart-UPS that have Network Management Cards installed you could connect each to the Network and then install PowerChute Network Shutdown (PCNS). PCNS will monitor up to 4 UPS a a time.

I have seen a few post on the APCUPSD forum / list group where people are attempting to monitor multiple UPS (Smart-UPS and Back-UPS) from a single system. I don't recall the thread/s but APCUPSD my be a solution for you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:46 AM . Last Modified: ‎2024-03-27 02:09 AM

0 Likes
0
1338
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:46 AM . Last Modified: ‎2024-03-27 02:09 AM

Thanks Bill,

It looks promising, but I'll have to play with it abit to see if it will do what I'm looking for. I'm configuring it now, hopefully this will do the job. If you have a computer running your entire house, you have to make sure it's rock solid, AND keep a close eye on it lol.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:46 AM . Last Modified: ‎2024-03-27 02:09 AM

0 Likes
0
1338
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:46 AM . Last Modified: ‎2024-03-27 02:09 AM

Well so far I haven't been able to get APCUPSD to recognise either one of my UPS's, let alone both. I've read every one of the install guides, tried every setting in the config file, etc. Both work fine with the PowerChute software, just can't monitor both at the same time, on the same machine that way 😞

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:47 AM . Last Modified: ‎2024-03-27 02:09 AM

0 Likes
0
1338
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:47 AM . Last Modified: ‎2024-03-27 02:09 AM

Hi,

Since you are using Back-UPS communications must be over USB.  Did you install the APCUPSD USB driver? On Windows when I have install APCUPSD it asks me if I want to install the needed driver but the installation fails so I have to follow the instruction listed in install.txt to load the driver manually. The file install.txt is normally found in C:\apcupsd\driver. Once the driver is loaded communications is established. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:47 AM . Last Modified: ‎2024-03-27 02:09 AM

0 Likes
0
1339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:47 AM . Last Modified: ‎2024-03-27 02:09 AM

I have it configured for USB, along with all the other recommended settings for USB type in the configuration file but no dice. The latest versions are preconfigured for USB devices anyways, but I verified everything matched the instructions none the less. I'm not 100% on the driver. I see the driver.ini file and I installed it. I can either of the UPS's to show up in device manager under BOTH batteries AND HID dvices, but still no communication. I manually specified the driver as instructed, and when it finishes, device manager shows a driver date of 2006/Microsoft. I have repeated this process many times,using every trickI can think of with the same results. I've uninstalled and reinstalled APCUPSD, restarted the server, etc. When I run the APCTEST utility (with APCUPSD services stopped) it always comes back with a fatal error during port configuration at line 321.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore