Model 1400 left load lights flashing

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Model 1400 left load lights flashing
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

0 Likes
8
1497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

Model 1400 left load lights flashing

I just replaced the batteries on a SmartUPS 1400 (the floor model, two battery) and the left load lights are flashing every now and then. What does this mean?

Thanks

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • 1400
  • apc
  • error
  • flashing
  • smartups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

I tried a USB to serial converter and that worked.

When sending the "Shift + A" everything lights up and the "beep" sounds. Not sure why I couldn't get "Shift + A" to work earlier since it worked on the rack mounted UPS. The load lights are still dead.

So some success. ๐Ÿ™‚

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

Hi,

I'd like to know, before you replace the battery, what indicators were flashing from the unit?

When you're facing the UPS is that the far left or far way right side that is flashing?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

The left hand side when facing the unit (load LED's) started flashing about every 5 seconds after I replaced the batteries. The batteries were dead and were so indicated by the replace battery indicator. As of today (Friday) the load LED's are no longer lit at all?!?!

Unit seems to still be working.

As of Saturday I pulled the plug and took out the batteries then hit the power button. After the reset the unit worked for maybe 5 minutes then the load lights started flashing again and then they went out again. Unit still seems to work.

Next I shut the UPS down and looked over the circuit board. The ESR on C31 and C35 seems high so I'll be replacing them.

Sunday... C37 is totally dead according to ESR measurements....


Ordered caps should be here is a week or so.

thanks

Message was edited by: husk

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

I have an APC 1500 Smart UPS that has the same (similar) problem with the Load Indicator Lights. None of them illuminate. However... in addition to that... two of my devices plugged into this battery backup would power off every 3-4 days. But the 3rd device (my server machine) continues to run without interruption.
Nemo

Message was edited by: Nemo

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

For a test I would increase or decrease the load on the unit but the indicators never light up. I've got another battery (which sits near the first one) that has the indicator lights working. When I increase the load on that device (by adding some equipment) you see the load indicator light up additional lights.
Is it safe to assume that this device has something failing in the control circuits?
There are no red lights or change battery lights lit on this unit.
Nemo

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

Any thoughts guys? and gals?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

I replaced the three caps. Two where probably bad, one was differently bad.

It appears the load light has finished dying. IE it no longer even flickers.

Anyone have any thoughts?

cheers

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

Yes the Load LEDS are dead.

I tried the serial connection and while I can connect to a rack mounted APC I have, I can't get the 1400 to respond.

Thoughts?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

0 Likes
0
1497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 09:01 PM . Last Modified: โ€Ž2024-03-20 05:52 AM

I tried a USB to serial converter and that worked.

When sending the "Shift + A" everything lights up and the "beep" sounds. Not sure why I couldn't get "Shift + A" to work earlier since it worked on the rack mounted UPS. The load lights are still dead.

So some success. ๐Ÿ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of