Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84426members
353619posts

Making the UTS6 work with the Honda eu2000i

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
rgsherr_apc
Crewman
Crewman
0 Likes
2
191

Making the UTS6 work with the Honda eu2000i

This was originally posted on APC forums on 10/4/2016


I've read through all the posts but still looking for a clear answer.  I have a Honda eu2000i and I'd like to use an  APC  transfer switch.  The UTS6H evidently connects and works fine but it doesn't appear to be in production anymore and doesn't seem to be any longer available anywhere. I don't understand why APC has discontinued it since the Honda eu2000i is an extremely popular generator but that's another question.  What I need to know is can I make the UTS6 work with with the eu2000i?  If so how? Is all I have to do is connect the two hot legs and use the PL530L1430 from cordtec.com to make it work?

Tags (3)

Accepted Solutions
RussellB_apc
Ensign
Ensign
0 Likes
0
191

Re: Making the UTS6 work with the Honda eu2000i

This was originally posted on APC forums on 7/3/2017


This suggestion is great with the caveat that future more powerful 120 volt generators will be limited by the 15amps the UPS inlet is rated to handle, correct?

See Answer In Context

2 Replies 2
wayne_i_apc
Lieutenant
Lieutenant
0 Likes
0
191

Re: Making the UTS6 work with the Honda eu2000i

This was originally posted on APC forums on 10/15/2016


Also see my response to your question at http://forums.apc.com/spaces/15/universal-transfer-switch/forums/general/7949/how-to-connect-a-honda...

Since the Honda EU2000I is rated at 13A, I would suggest that the easiest solution would be to connect the generator to the UPS inlet on the front of the UTS. You would need to set the outputs to use "UPS" for the "Source", and may need to change some other settings to get the best operation. This would result in no output from the UTS 240V output (circuits 5&6 on the UTS6BI and 9&10 on the UTS10BI) and circuit 1 (normally reserved for powering a UPS), but all other 120V outputs should function normally.

RussellB_apc
Ensign
Ensign
0 Likes
0
192

Re: Making the UTS6 work with the Honda eu2000i

This was originally posted on APC forums on 7/3/2017


This suggestion is great with the caveat that future more powerful 120 volt generators will be limited by the 15amps the UPS inlet is rated to handle, correct?