MGE Galaxy 5000 - XMB07 control connection for external battery cabinet

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • MGE Galaxy 5000 - XMB07 control connection for external battery cabinet
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:33 PM . Last Modified: ‎2024-03-20 04:08 AM

0 Likes
4
2986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:33 PM . Last Modified: ‎2024-03-20 04:08 AM

MGE Galaxy 5000 - XMB07 control connection for external battery cabinet

Hi,

I have a problem with an MGE Galaxy 5000 - 80kVA UPS with external battery cabinet and an external battery breaker cabinet, I have installed and operated the UPS and all is fine except one problem, the battery breaker is always tripped!

According to the attached file and my case of 1 battery cabinet, on the XMB07 the coil of the circuit breaker (terminals 1 and 2 of the Battery breaker cabinet/battery disconnect) should be connected to terminals 1 and 3 of the XMB07, the breaker is tripped when no voltage is present on the coil terminals, so in normal operation it should be always energized, but there is no voltage on the XMB07 terminals 1 and 3 so the breaker is always tripped.

There is no alarm whatsoever on the UPS, and the menus showing the battery status and/or test commands are not there! Is this normal? Do I have a faulty UPS or did I do something wrong?

Message was edited by: takamul

Attachments
Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-29 09:34 PM . Last Modified: ‎2024-03-20 04:07 AM

0 Likes
0
2981
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:34 PM . Last Modified: ‎2024-03-20 04:07 AM

Have you tried shutting down the UPS and with no wires connected to XMB007 or XMB008 seeing what the voltage is on pin 1/3 on XMB007 and XMB008? Do you have the jumper installed in XMB006?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-29 09:33 PM . Last Modified: ‎2024-03-20 04:08 AM

0 Likes
0
2981
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:33 PM . Last Modified: ‎2024-03-20 04:08 AM

If you are looking at XMB007 plugged into the UPS are your wires landed in the top of the terminal in order 1, 2, 3? If you pull the XMB007 connector out you will see a small arrow on the UPS where the connector plugs in, that arrow points to pin 1. So looking at the connector plugged in, the Bottom pin is 1 and you land 2 above that and 3 above that with pin 4 at the top of the connector, nothing plugged in.

So imagine this is the connector
XMB008 Connector
4 - Open
3- Open
2- Open
1- Open

XMB007
4- open
3- Orange wire
2- Red Wire
1 -Brown wire

XMB006
2-Jumper Or External connection to EPO
1-Jumper Or external connection to EPO

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:34 PM . Last Modified: ‎2024-03-20 04:07 AM

0 Likes
0
2981
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:34 PM . Last Modified: ‎2024-03-20 04:07 AM

The numbering plan is correct and so is our connection, but the issue is that the 1 and 3 should be the coil command output (24V), meaning the trip coil of the battery breaker ( I have an external battery cabinet) should be high (24V) and if there is a trouble it should be 0V, but the situation is that the output on 1 and 3 is always 0V which makes the breaker always tripped!!

In addition, all the menus related to the battery measurements or status do not exist on the lcd console!

Do you have any suggestions?

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-29 09:34 PM . Last Modified: ‎2024-03-20 04:07 AM

0 Likes
0
2981
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:34 PM . Last Modified: ‎2024-03-20 04:07 AM

I would call your local APC office for further assistance.

The MGE Galaxy should always only be started up by Trained and Authorized personnel with the proper software to program the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-29 09:34 PM . Last Modified: ‎2024-03-20 04:07 AM

0 Likes
0
2982
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:34 PM . Last Modified: ‎2024-03-20 04:07 AM

Have you tried shutting down the UPS and with no wires connected to XMB007 or XMB008 seeing what the voltage is on pin 1/3 on XMB007 and XMB008? Do you have the jumper installed in XMB006?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore