Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84702members
354079posts

MGE Galaxy 5000 - XMB07 control connection for external battery cabinet

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
4
674

MGE Galaxy 5000 - XMB07 control connection for external battery cabinet

This question was originally posted by Yamen on APC forums on 12/11/2010


Hi,

I have a problem with an MGE Galaxy 5000 - 80kVA UPS with external battery cabinet and an external battery breaker cabinet, I have installed and operated the UPS and all is fine except one problem, the battery breaker is always tripped!

According to the attached file and my case of 1 battery cabinet, on the XMB07 the coil of the circuit breaker (terminals 1 and 2 of the Battery breaker cabinet/battery disconnect) should be connected to terminals 1 and 3 of the XMB07, the breaker is tripped when no voltage is present on the coil terminals, so in normal operation it should be always energized, but there is no voltage on the XMB07 terminals 1 and 3 so the breaker is always tripped.

There is no alarm whatsoever on the UPS, and the menus showing the battery status and/or test commands are not there! Is this normal? Do I have a faulty UPS or did I do something wrong?

Message was edited by: takamul

Attachments

Accepted Solutions
upsguy_apc
Commander
Commander
0 Likes
0
674

Re: MGE Galaxy 5000 - XMB07 control connection for external battery cabinet

This was originally posted on APC forums on 12/15/2010


Have you tried shutting down the UPS and with no wires connected to XMB007 or XMB008 seeing what the voltage is on pin 1/3 on XMB007 and XMB008? Do you have the jumper installed in XMB006?

See Answer In Context

4 Replies 4
upsguy_apc
Commander
Commander
0 Likes
0
674

Re: MGE Galaxy 5000 - XMB07 control connection for external battery cabinet

This was originally posted on APC forums on 12/11/2010


If you are looking at XMB007 plugged into the UPS are your wires landed in the top of the terminal in order 1, 2, 3? If you pull the XMB007 connector out you will see a small arrow on the UPS where the connector plugs in, that arrow points to pin 1. So looking at the connector plugged in, the Bottom pin is 1 and you land 2 above that and 3 above that with pin 4 at the top of the connector, nothing plugged in.

So imagine this is the connector
XMB008 Connector
4 - Open
3- Open
2- Open
1- Open

XMB007
4- open
3- Orange wire
2- Red Wire
1 -Brown wire

XMB006
2-Jumper Or External connection to EPO
1-Jumper Or external connection to EPO

BillP
Administrator Administrator
Administrator
0 Likes
0
674

Re: MGE Galaxy 5000 - XMB07 control connection for external battery cabinet

This reply was originally posted by Yamen on APC forums on 12/13/2010


The numbering plan is correct and so is our connection, but the issue is that the 1 and 3 should be the coil command output (24V), meaning the trip coil of the battery breaker ( I have an external battery cabinet) should be high (24V) and if there is a trouble it should be 0V, but the situation is that the output on 1 and 3 is always 0V which makes the breaker always tripped!!

In addition, all the menus related to the battery measurements or status do not exist on the lcd console!

Do you have any suggestions?

upsguy_apc
Commander
Commander
0 Likes
0
674

Re: MGE Galaxy 5000 - XMB07 control connection for external battery cabinet

This was originally posted on APC forums on 12/14/2010


I would call your local APC office for further assistance.

The MGE Galaxy should always only be started up by Trained and Authorized personnel with the proper software to program the UPS.

upsguy_apc
Commander
Commander
0 Likes
0
675

Re: MGE Galaxy 5000 - XMB07 control connection for external battery cabinet

This was originally posted on APC forums on 12/15/2010


Have you tried shutting down the UPS and with no wires connected to XMB007 or XMB008 seeing what the voltage is on pin 1/3 on XMB007 and XMB008? Do you have the jumper installed in XMB006?