I have the LE1200 voltage switch set at 120V. If I measure 117.5VAC at the wall I also measure 117.5VAC from the LE1200. I thought the LE1200 is supposed to output 120VAC. I got this because I thought a voltage regulator would keep my AC at a steady 120V. Is this considered "normal" operating range?
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:28 AM . Last Modified: 2024-03-27 12:58 AM
Hi Jimme,
The LE1200 will only intervene when the input voltage leaves an acceptable voltage window. Intervention means boosting or trimming the input voltage by a fixed percentage to keep the output within the acceptable window (but not exactly 120V). You can find specifications here and the manual here.
The manual says regulation is +6% to -12%. At 120V, that corresponds to an acceptable output range of 106V-127V. This is also the default acceptable output range on the SmartUPS UPSes.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:28 AM . Last Modified: 2024-03-27 12:58 AM
Hi Jimme,
The LE1200 will only intervene when the input voltage leaves an acceptable voltage window. Intervention means boosting or trimming the input voltage by a fixed percentage to keep the output within the acceptable window (but not exactly 120V). You can find specifications here and the manual here.
The manual says regulation is +6% to -12%. At 120V, that corresponds to an acceptable output range of 106V-127V. This is also the default acceptable output range on the SmartUPS UPSes.