Posted: 2021-06-28 05:06 AM . Last Modified: 2024-03-27 01:14 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:06 AM . Last Modified: 2024-03-27 01:14 AM
I have Cisco network POE switches plugged into a 9-port APC SurgeArrest unit. The SurgeArrest unit is plugged into an APC UPS model (SMX7500RM2U/SMX48RMBP2U).
The Fault Protection indicator was illuminated. When performing troubleshooting, I turned off the SurgeArrest device and removed the devices plugged into it. I then turned the SurgeArrest back on - the Fault Protection indicator on the SurgeArrest device was not lit.
I then plugged in one device at a time into the SurgeArrest. About one minute after I plugged in the last device (filling the device ports in the back of the unit) the Fault Protection light illuminated. I performed multiple tests plugging in the devices one at a time using a different sequence each time. Again the Fault light illuminated after the last deivce was plugged in.
I am trying to determine the cause of this and a resolution.
Can you give me any advice?
Thank you,
Gary
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:06 AM . Last Modified: 2024-03-27 01:14 AM
Hello Gary,
It looks like you are daisy chaining a surge protector from a UPS. This is not recommended, nor necessary. All of our UPSs have surge protection built in. The UPS output design prevents the surge protector from seeing a good path to ground, so it displays that it doesnt have protection, since out surge protectors (and UPSs) work by shunting excess energy through the ground.
I would recommend plugging the surge protector directly into the wall and then plugging non-essential equipment and any data lines you want to protect into the surge protector. Everything else can be plugged into the UPS.
Thanks,
Shanon
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:06 AM . Last Modified: 2024-03-27 01:14 AM
Gary,
What is the model number of the surge arrest?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:06 AM . Last Modified: 2024-03-27 01:14 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:06 AM . Last Modified: 2024-03-27 01:14 AM
Bill,
The model number is NET9RMBLK. Thanks for responding.
- Gary
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:06 AM . Last Modified: 2024-03-27 01:14 AM
Hello Gary,
It looks like you are daisy chaining a surge protector from a UPS. This is not recommended, nor necessary. All of our UPSs have surge protection built in. The UPS output design prevents the surge protector from seeing a good path to ground, so it displays that it doesnt have protection, since out surge protectors (and UPSs) work by shunting excess energy through the ground.
I would recommend plugging the surge protector directly into the wall and then plugging non-essential equipment and any data lines you want to protect into the surge protector. Everything else can be plugged into the UPS.
Thanks,
Shanon
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:06 AM . Last Modified: 2024-03-27 01:14 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:06 AM . Last Modified: 2024-03-27 01:14 AM
Thank you for the detailed explanation. I appreciate your prompt response.
- Gary