Is the UTS10BI right for my application?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Is the UTS10BI right for my application?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Janeway Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:19 PM . Last Modified: ‎2024-03-20 03:05 AM

0 Likes
2
712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:19 PM . Last Modified: ‎2024-03-20 03:05 AM

Is the UTS10BI right for my application?

I just purchased a Honda EU6500is generator to provide critical backup during power outages such as we've experienced recently here in NJ.

My house is all electric:

1/2 HP well pump 240V (Running: 6amps , LRA/C: 23amps)
40 gallon HW heater 4500W
16 cu ft. refrigerator 5.5 running amps
Kitchen Aid convection oven 1440W
Electric range: 8" burner
Compact fluorescent lights
Computer 480W PSU
21-inch monitor
APC Smart 700 UPS
HP LaserJet 2100
Etc.

Obviously, I could never power all of these loads at the same time; however, I would like to manage them preferably through the UTS10BI with ALM (shedding) or, if not possible, manually through the use of a service panel Interlock kit.

I understand that the UTS10BI cannot handle more than one 240V load through Circuits #9 and #10. So, I thought about wiring the well pump, HW heater, and electric range to Circuits #9 and #10 and then install “manual” switches between the HW heater, electric range, and well pump to manually disconnect them from the above-referenced circuits. Doing so would allow me to connect them as needed with only one on Circuits #9 and #10 at a given time.

My greatest concern is that the 20amp fuse of Circuits #9 and #10 might not even handle the loads individually!

My question as I stated above, could I wire the well pump, the HW heater, and the electric range into Circuits #9 and #10 and only have one connected at a given time? I would prefer to leave the well pump “manual” switch set to “ON” and only turn off the well pump when I needed to provide power to either the HW heater or range.

Also, I would like the refrigerator (120V) to run most of the time and the well pump (240V) as needed with the UTS10BI handling these two automatically. It's the Locked Rotor Amps/Current that concerns me. If the refrigerator and the well pump happen to turn on at the same time would the inrush current (LRA/C) be too much for the generator/UTS to handle?

I've been told by those supposedly informed that the well pump and refrigerator should not cause any problem for the generator or the UTS10BI, but I'm concerned that the UTS10BI might refuse to provide power given a 20amp fuse on Circuits #9 and #10. In addition, the well pump is on a 30amp breaker as is the HW heater.

The well pump installer told me the 30amp breaker was more for convenience and that the pump motor would never draw anywhere near that amount of current (running 6amps; inrush 23amps). If the 30amp breaker is not required, could I replace with a 20amp breaker? Similarly, is the HW heater out of the question, since I believe it requires a 30amp breaker, or am I incorrect?

I would be most appreciative if senior members et al. would help me decide which path to take: UTS10BI or an Interlock kit. If I have to manually manage the loads, I would prefer an Interlock kit over a manual transfer switch, because I could use the breakers in the service panel to control all house circuits, of course being mindful not to overload any.

whp

Message was edited by: whp

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:19 PM . Last Modified: ‎2024-03-20 03:05 AM

0 Likes
0
712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:19 PM . Last Modified: ‎2024-03-20 03:05 AM

I just purchased a Honda EU6500is generator to provide critical backup during power outages such as we've experienced recently here in NJ.

My house is all electric:

1/2 HP well pump 240V (Running: 6amps , LRA/C: 23amps)
40 gallon HW heater 4500W
16 cu ft. refrigerator 5.5 running amps
Kitchen Aid convection oven 1440W
Electric range: 8" burner
Compact fluorescent lights
Computer 480W PSU
21-inch monitor
APC Smart 700 UPS
HP LaserJet 2100
Etc.

Obviously, I could never power all of these loads at the same time; however, I would like to manage them preferably through the UTS10BI with ALM (shedding) or, if not possible, manually through the use of a service panel Interlock kit.

I understand that the UTS10BI cannot handle more than one 240V load through Circuits #9 and #10. So, I thought about wiring the well pump, HW heater, and electric range to Circuits #9 and #10 and then install “manual” switches between the HW heater, electric range, and well pump to manually disconnect them from the above-referenced circuits. Doing so would allow me to connect them as needed with only one on Circuits #9 and #10 at a given time.

My greatest concern is that the 20amp fuse of Circuits #9 and #10 might not even handle the loads individually!

My question as I stated above, could I wire the well pump, the HW heater, and the electric range into Circuits #9 and #10 and only have one connected at a given time? I would prefer to leave the well pump “manual” switch set to “ON” and only turn off the well pump when I needed to provide power to either the HW heater or range.

Also, I would like the refrigerator (120V) to run most of the time and the well pump (240V) as needed with the UTS10BI handling these two automatically. It's the Locked Rotor Amps/Current that concerns me. If the refrigerator and the well pump happen to turn on at the same time would the inrush current (LRA/C) be too much for the generator/UTS to handle?

I've been told by those supposedly informed that the well pump and refrigerator should not cause any problem for the generator or the UTS10BI, but I'm concerned that the UTS10BI might refuse to provide power given a 20amp fuse on Circuits #9 and #10. In addition, the well pump is on a 30amp breaker as is the HW heater.

The well pump installer told me the 30amp breaker was more for convenience and that the pump motor would never draw anywhere near that amount of current (running 6amps; inrush 23amps). If the 30amp breaker is not required, could I replace with a 20amp breaker? Similarly, is the HW heater out of the question, since I believe it requires a 30amp breaker, or am I incorrect?

I would be most appreciative if senior members et al. would help me decide which path to take: UTS10BI or an Interlock kit. If I have to manually manage the loads, I would prefer an Interlock kit over a manual transfer switch, because I could use the breakers in the service panel to control all house circuits, of course being mindful not to overload any.

whp

Message was edited by: whp

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:19 PM . Last Modified: ‎2024-03-20 03:05 AM

0 Likes
0
712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:19 PM . Last Modified: ‎2024-03-20 03:05 AM

You wrote, "I understand that the UTS10BI cannot handle more than one 240V load through Circuits #9 and #10." It is my impression, however, (APC User Manual for the UTS10B1, page 1-3, "Supporting 240V circuits") that "multiple 240V loads can be wired to that 240V circuit if required."

Have I misunderstood?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:19 PM . Last Modified: ‎2024-03-20 03:05 AM

0 Likes
0
713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:19 PM . Last Modified: ‎2024-03-20 03:05 AM

I just purchased a Honda EU6500is generator to provide critical backup during power outages such as we've experienced recently here in NJ.

My house is all electric:

1/2 HP well pump 240V (Running: 6amps , LRA/C: 23amps)
40 gallon HW heater 4500W
16 cu ft. refrigerator 5.5 running amps
Kitchen Aid convection oven 1440W
Electric range: 8" burner
Compact fluorescent lights
Computer 480W PSU
21-inch monitor
APC Smart 700 UPS
HP LaserJet 2100
Etc.

Obviously, I could never power all of these loads at the same time; however, I would like to manage them preferably through the UTS10BI with ALM (shedding) or, if not possible, manually through the use of a service panel Interlock kit.

I understand that the UTS10BI cannot handle more than one 240V load through Circuits #9 and #10. So, I thought about wiring the well pump, HW heater, and electric range to Circuits #9 and #10 and then install “manual” switches between the HW heater, electric range, and well pump to manually disconnect them from the above-referenced circuits. Doing so would allow me to connect them as needed with only one on Circuits #9 and #10 at a given time.

My greatest concern is that the 20amp fuse of Circuits #9 and #10 might not even handle the loads individually!

My question as I stated above, could I wire the well pump, the HW heater, and the electric range into Circuits #9 and #10 and only have one connected at a given time? I would prefer to leave the well pump “manual” switch set to “ON” and only turn off the well pump when I needed to provide power to either the HW heater or range.

Also, I would like the refrigerator (120V) to run most of the time and the well pump (240V) as needed with the UTS10BI handling these two automatically. It's the Locked Rotor Amps/Current that concerns me. If the refrigerator and the well pump happen to turn on at the same time would the inrush current (LRA/C) be too much for the generator/UTS to handle?

I've been told by those supposedly informed that the well pump and refrigerator should not cause any problem for the generator or the UTS10BI, but I'm concerned that the UTS10BI might refuse to provide power given a 20amp fuse on Circuits #9 and #10. In addition, the well pump is on a 30amp breaker as is the HW heater.

The well pump installer told me the 30amp breaker was more for convenience and that the pump motor would never draw anywhere near that amount of current (running 6amps; inrush 23amps). If the 30amp breaker is not required, could I replace with a 20amp breaker? Similarly, is the HW heater out of the question, since I believe it requires a 30amp breaker, or am I incorrect?

I would be most appreciative if senior members et al. would help me decide which path to take: UTS10BI or an Interlock kit. If I have to manually manage the loads, I would prefer an Interlock kit over a manual transfer switch, because I could use the breakers in the service panel to control all house circuits, of course being mindful not to overload any.

whp

Message was edited by: whp

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of