Is it okay to connect my APC BX1400U-MS to a stabilizer?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Is it okay to connect my APC BX1400U-MS to a stabilizer?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
121
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:09 PM . Last Modified: ‎2024-03-26 02:50 AM

0 Likes
1
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:09 PM . Last Modified: ‎2024-03-26 02:50 AM

Is it okay to connect my APC BX1400U-MS to a stabilizer?

I have a BX1400U-MS. The UPS operating range is between 150 - 280 volts. The reason I'm asking this question is because my AC power source in my neighborhood is a bit unstable right now, to say the least. Undervoltage below 150 volt coupled with blackout is as normal as breathing these days, it's ridiculous, so my UPS is switching to battery mode very often, to the point the charging can't keep up, forcing a shut down. I've set the Sensitivity settings to Low.

I've filed a complaint to the electric company and they said they're going to look into it ASAP. However, knowing their average response time, it will probably take days before they can actually get here and fix the problem. That's why I'm looking for a temporary solution for this, because I need the UPS to keep my PC alive when I'm working.

So, is it okay to connect my UPS to a stabilizer so the UPS will hopefully stop switching to battery mode?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • back-ups
  • noise
  • question
  • ups
  • voltage
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:09 PM . Last Modified: ‎2024-03-26 02:50 AM

0 Likes
0
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:09 PM . Last Modified: ‎2024-03-26 02:50 AM

I believe you have to think as they say "out of the box" , your problem doesn't look to be fixed by connecting your UPS to a stabilizer and right now you are close to destroy your batteries with this often charge discharge cycle.

Look at this video that some one sent me because I think it would help you in the mean time. 

https://youtu.be/1q4dUt1yK0g

As I was looking your UPS and it seems to came with 2 batteries of 7.2 A/h. If by any chance you have to replace them, use instead the 9 A/h type which are the same size and could give you a bit more remaining time.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:09 PM . Last Modified: ‎2024-03-26 02:50 AM

0 Likes
0
1963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:09 PM . Last Modified: ‎2024-03-26 02:50 AM

I believe you have to think as they say "out of the box" , your problem doesn't look to be fixed by connecting your UPS to a stabilizer and right now you are close to destroy your batteries with this often charge discharge cycle.

Look at this video that some one sent me because I think it would help you in the mean time. 

https://youtu.be/1q4dUt1yK0g

As I was looking your UPS and it seems to came with 2 batteries of 7.2 A/h. If by any chance you have to replace them, use instead the 9 A/h type which are the same size and could give you a bit more remaining time.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore