Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

International UPS Power Backup

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • International UPS Power Backup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-22 02:57 AM

0 Likes
2
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-22 02:57 AM

International UPS Power Backup

Hello Friends.

I'm in need of a UPS power backup that will work in the USA and overseas. I am a professional pianist and composer. I also record and produce my music and I work with a variety of musicians from other parts of the world. My computer will work with a wide range of voltage inputs, but other items like my headphone amp or multitrack recorder only accepts 120v input. I would like to be able to plug everything into one UPS backup and have them all work.

I have searched the web trying to find something that will accept an input of 100-240v and output 120v, but so far I have been unsuccessful. Does anyone have any ideas or solutions that may work? Also, can I buy an APC UPS that is rated with an input of 240v with an output of 240v and bring it to the USA and plug it into a 120v source with successful results? I have tried this with other devices and in some cases they still functioned.


Steve
http://www.sanddust.com

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Erasmus_apc
Contributor

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-22 02:57 AM

0 Likes
0
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-22 02:57 AM

Hi,

APC has an X167 selection of units (rather limited) such as SU2200R3X167 (2200VA) and SU700X167 (750VA). These units take 120v or 230v input, and output 120v only. Their input ranges are: 187 - 242 (220V), and 92 - 147V. They can also accept input cords such as:

British BS1363A
Italian CEI 23-16
NEMA 5-15P
Schuko CEE 7/7P

These units are Smart-UPS, so they have the same benefits in terms of accessory cards and superior performance that our other Smart-UPS offer.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-22 02:57 AM

0 Likes
0
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-22 02:57 AM

In Brazil we have a company called TS SHARA, that makes a full range UPS model. It works from 84-250V and puts out 115V +/- 6%.

UPS Soho II 800 1BS full-range:

http://tsshara.com.br/nobreak_soho.php

It is an 800VA UPS

Message was edited by: rau

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Erasmus_apc
Contributor

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-22 02:57 AM

0 Likes
0
1231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-22 02:57 AM

Hi,

APC has an X167 selection of units (rather limited) such as SU2200R3X167 (2200VA) and SU700X167 (750VA). These units take 120v or 230v input, and output 120v only. Their input ranges are: 187 - 242 (220V), and 92 - 147V. They can also accept input cords such as:

British BS1363A
Italian CEI 23-16
NEMA 5-15P
Schuko CEE 7/7P

These units are Smart-UPS, so they have the same benefits in terms of accessory cards and superior performance that our other Smart-UPS offer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore