I have Smart-UPS 1000 and 6.5KVA Generator. But UPS don't work with Generator Power
how to adjust the UPS to work with Generator.
Thanks
------------------------------------------------------- E D I T -----------------------------------------------------------
I find out the solution:-
Adjusting Power Parameters in PowerChute to Medium Sensitivity.
Tested Working Fine with Generator
Message was edited by: mujeebas
Message was edited by: mujeebas
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-26 12:02 AM
good to hear. lowering sensitivity is the first thing to do when having an issue with a generator.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-26 12:03 AM
check my reply on your other thread 😉
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-26 12:02 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-26 12:02 AM
I have problem also. Now I using APC5K and Generator 5,5KVA. Please help us !
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-26 12:02 AM
good to hear. lowering sensitivity is the first thing to do when having an issue with a generator.