High end system, please suggest a suitable APC UPS

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • High end system, please suggest a suitable APC UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
rickey_apc
Crewman rickey_apc
Crewman

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:46 AM

0 Likes
8
1538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:46 AM

High end system, please suggest a suitable APC UPS

Greetings

I'm building a new system

and I'd like to use a proper APC UPS with it.

Specs:

CPU: Intel i7 4790k

VGA: GTX 780 Ti  (MSI GTX 780Ti GAMING 3G)

HD: 1 high rpm sata3

SSD: 1 SSD M.2

PSU: 1000W 80+ Platinum (EVGA SuperNOVA 1000 P2)

Monitor LCD 24"

Modem/Router



I already have an old APC Back-UPS RS 800,

but,  I think that it's not proper for my new system,

plus that it's previous battery had died, and I would need to buy another one, in order to use it.




Please suggest me a suitable APC UPS.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:45 AM

0 Likes
0
1539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:45 AM

One of the items to consider is how fast the UPS will cut in when there is a power event. I had built a system a couple of years back with an Antec power supply and found that the UPS couldn't cut in fast enough to prevent the system from bouncing. I ended up purchasing a double-conversion 1500VA UPS. That type of UPS is more expensive, but it provides better protection.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
rickey_apc
Crewman rickey_apc
Crewman

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:46 AM

0 Likes
0
1538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:46 AM

Greetings

I'm building a new system

and I'd like to use a proper APC UPS with it.

Specs:

CPU: Intel i7 4790k

VGA: GTX 780 Ti  (MSI GTX 780Ti GAMING 3G)

HD: 1 high rpm sata3

SSD: 1 SSD M.2

PSU: 1000W 80+ Platinum (EVGA SuperNOVA 1000 P2)

Monitor LCD 24"

Modem/Router



I already have an old APC Back-UPS RS 800,

but,  I think that it's not proper for my new system,

plus that it's previous battery had died, and I would need to buy another one, in order to use it.




Please suggest me a suitable APC UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:46 AM

0 Likes
0
1538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:46 AM

Hi,

I recommend our Smart-UPS SMT2200i If your power supply can draw 1000W you would want a UPS that can handle a large load. You could utilize a smaller SMT if you know that the power supply will never be drawing its full capacity. The next smaller SMT model is the SMT1000i and its maximum load is 1000W

Note: with the SMT2200i you will need 20 amp input.

Reply

Link copied. Please paste this link to share this article on your social media post.

rickey_apc
Crewman rickey_apc
Crewman

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:45 AM

0 Likes
0
1538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:45 AM

Thanks for trying to help, but I think that both your suggestions are not appropriate for my system (the first is too much, the latter too small)

About the Smart-UPS SMT2200i:

based on it's specs page https://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SMT2200I

it says that it has Output Power Capacity: 1980 Watts

which is double my PSU's maximum output .

Also, the next smaller SMT model, which you suggest, SMT1000i,

in it's specs page https://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SMT1000I

it says that it has Output Power Capacity 700 Watts,

which doesn't match the "maximum load is 1000W" that you wrote.

I thing that a proper UPS should be of 1300 VA,

which based on the rule of thumb W = 0.6 * VA   the wattage rating of a UPS is approximately 0.6 * its VA rating)

should give 780W, that, it's around my system's power consumption, as I estimate it.

Am I wrong?

Reply

Link copied. Please paste this link to share this article on your social media post.

smargh_apc
Ensign smargh_apc
Ensign

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:45 AM

0 Likes
0
1538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:45 AM

  • It's best practice to keep a UPS at 50% max load.
  • PSU input power is higher than output power.
  • Which UPS is appropriate for you depends on your anticipated highest PSU input power requirements.

Personally I think a SURT1000XL(I) or SURT2000XL(I) would be nice if you have the money or can find one 2nd hand, or perhaps especially if you have dirty regional power, but it does depend on your expected maximum loaded power requirements.

I also don't think you need a 1000W PSU for that kit, unless you'll be adding more graphics cards or adding extra kit in the future. PSU efficiency is slighly lower at less load.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:45 AM

0 Likes
0
1538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:45 AM

Not sure if you've considered seeing what the APC UPS Selector spits out yet?

UPS Selector - Select your protection needs

Reply

Link copied. Please paste this link to share this article on your social media post.

roger_apc
Ensign roger_apc
Ensign

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:45 AM

0 Likes
0
1539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:45 AM

What the "name plate" rating of the power supply say, and what the actual power requirements are, can (and usually are) vastly different.  We have multiple(8+) servers (HP Proliant 380 G8 and Dell Power Edge 2950) each with a PS rating of 500 watts or more each running on metered PDU's.  In fact, each one draws about 100 watts of power.

Imagine (10) 100 watt light bulbs sitting on or under your desk.  That would be a lot of heat!  Now put your hand close to wherever the air is being exhausted from your system.  Does that even feel close?  All of the energy (with reasonable measurement methods) that is put into a computer system is translated into heat.  Think about the fact that a really good electric heater (plug in type) will only be rated at 1800 watts (in North America).  Is your computer putting out anywhere close to that much heat?

I would bet that the actual load of your computer system will be (well) under 200 watts.  If you are in Southern California, I'd bet a steak dinner (you choose the place) on that.

Proceed as you see fit.  🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

rickey_apc
Crewman rickey_apc
Crewman

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:45 AM

0 Likes
0
1539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:45 AM

Yes, I've tried the APC UPS Selector and it gives 261W, and that's without the VGA.

For the VGA, In it's specs page it says that it's power consumption is 250W.

Therefore we go to 261W+250W=511W (plus the consumption of a modem/router).


That's what the UPS Selector suggests for Load Requirements of 550W:

Best Price: SMC1000I

Best Value: SMT1000I

Best Performance: BR1500GI

2414_Screenshot %2819%29%7E.png



Therefore, will I'll be ok with a UPS of 1000VA ? (most probably SMC1000I because I don't think I can afford any bigger one)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:45 AM

0 Likes
0
1540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:50 PM . Last Modified: ‎2024-03-20 03:45 AM

One of the items to consider is how fast the UPS will cut in when there is a power event. I had built a system a couple of years back with an Antec power supply and found that the UPS couldn't cut in fast enough to prevent the system from bouncing. I ended up purchasing a double-conversion 1500VA UPS. That type of UPS is more expensive, but it provides better protection.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore