Galaxy 3000 10KVA

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Galaxy 3000 10KVA
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:37 PM . Last Modified: ‎2024-03-20 04:02 AM

0 Likes
5
2562
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:37 PM . Last Modified: ‎2024-03-20 04:02 AM

Galaxy 3000 10KVA

I just replaced all batteries of my UPS but still it gives Low battery alarm. I already charged it by an external charger before installing but same result..Need help..

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:37 PM . Last Modified: ‎2024-03-20 04:01 AM

0 Likes
0
2561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:37 PM . Last Modified: ‎2024-03-20 04:01 AM

Yes i replaced the batteries with new coz it was alarming as follows: End of battery life, Batteries or some cell are low.
I installed 48 batteries 12V 7Ah rating same specs with the old but different brand or type.
It is alarming when batt voltage at 315 supposed to be around 324 volts.
It displays Zero life for battery but strange because its showing 100% charged..
tnx for the info

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:37 PM . Last Modified: ‎2024-03-20 04:02 AM

0 Likes
0
2561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:37 PM . Last Modified: ‎2024-03-20 04:02 AM

hi there 220V,
I know that price is a factor which influence a lot. but, later down the road you will spend more money trying to replace batteries here and there, to patch your system.
So, advice : try to keep the same battery brand( you will get the same mechanical end electrical specs), the same date code on the battery, and also, since you're using small 12V7, try to get them no older than 6 months.
Also, the UPS counter has to be cleared ( get APC to do it), and the UPS will perform and autmatic battery test 24 hours from the moment when it "sees " them fully charged and counter set to 60 months.
If the test fail, you have bad batteries. And if that is true, this is when you are going to start spending more money.

you can try CSB or BB Battery. Personally I use GS and they are pretty good.

Regards,

M

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:37 PM . Last Modified: ‎2024-03-20 04:02 AM

0 Likes
0
2561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:37 PM . Last Modified: ‎2024-03-20 04:02 AM

it shows 100% charged on the display but the alarm still exist..I wonder if its enough to charge the battery by just putting the load on the bypass and leave the UPS charging? or maybe its necessary to switch off the load just to make sure the UPS is charging the batts? tnx

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:37 PM . Last Modified: ‎2024-03-20 04:02 AM

0 Likes
0
2561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:37 PM . Last Modified: ‎2024-03-20 04:02 AM

Yes i replaced the batteries with new coz it was alarming as follows: End of battery life, Batteries or some cell are low.
I installed 48 batteries 12V 7Ah rating same specs with the old but different brand or type.
It is alarming when batt voltage at 315 supposed to be around 324 volts.
It displays Zero life for battery but strange because its showing 100% charged..
tnx for the info

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-29 09:37 PM . Last Modified: ‎2024-03-20 04:01 AM

0 Likes
0
2561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:37 PM . Last Modified: ‎2024-03-20 04:01 AM

The UPS has a dedicated charging circuit and will not charge any faster in bypass or online. The Galaxy Line of UPS has an Internal type of "clock" that counts down from an initial setpoint, normally 48 or 60 months. Once this clock counts down to 0 it will require an APC engineer to reset this with specialized software.

I'm not sure if this is the exact alarm you are getting..

Did you replace your batteries initially as a result of this alarm?
What is the displayed battery voltage?
How many batteries do you have installed?
Did you replace with the same type as removed?
What type of battery do you have installed?
What is your load level?
What is the displayed battery runtime?
What is the Battery Service Lifetime in the battery measurements screen?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:37 PM . Last Modified: ‎2024-03-20 04:01 AM

0 Likes
0
2562
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:37 PM . Last Modified: ‎2024-03-20 04:01 AM

Yes i replaced the batteries with new coz it was alarming as follows: End of battery life, Batteries or some cell are low.
I installed 48 batteries 12V 7Ah rating same specs with the old but different brand or type.
It is alarming when batt voltage at 315 supposed to be around 324 volts.
It displays Zero life for battery but strange because its showing 100% charged..
tnx for the info

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore