Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84694members
354073posts

Emergency off button integrated to external system

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

H_ups
Cadet
0 Likes
1
431

Emergency off button integrated to external system

How does one integrate the emergency off button (EPO/EMO) circuit of an Smart-UPS SRT 5000 (SRT5KXLI) to an external system with its own 24V emergency off circuit?

 

There is some information in the manual about EPO but not how/if possible to connect to an external system.

 

Basically I want to use the existing emergency off button on the external system to also shut down the UPS at the same time.  

Tags (1)
1 Reply 1
Brad_C_apc
Commander
Commander
0 Likes
0
416

Re: Emergency off button integrated to external system

You'll want the external system to provide a dry contact output, either normally open or closed and wire it up the way it says on page 26 of the manual.

 

If the external system only provides some form of powered output, you'll want to put a relay between it and the UPS.

 