ES750 is triggering off (often) with tone for no noticeable reason

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • ES750 is triggering off (often) with tone for no noticeable reason
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
100
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:31 PM . Last Modified: ‎2024-03-20 04:11 AM

0 Likes
9
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:31 PM . Last Modified: ‎2024-03-20 04:11 AM

ES750 is triggering off (often) with tone for no noticeable reason

I have an ES750 in an equipment closet in my basement with a connected dsl modem, an Airport Extreme router, a DirecTV dvr and a Synology NAS connected.  For awhile now it has been triggering approx weekly turning off with the tone.  I know to look when I lose internet and, as I head to the basement, I hear the tone.  I hit the power button and everything fires back up.  This was happening weekly but now it seems to be happening multiple times in a day.  It's frustrating and is tempting me to just plug everything into a regular ol' power strip.  Is my 750 gone?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:32 PM . Last Modified: ‎2024-03-20 04:11 AM

0 Likes
0
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:32 PM . Last Modified: ‎2024-03-20 04:11 AM

And the DSL modem is connected to a Battery Backup + surge outlet vs. surge only?

Any feedback on my other questions - using PowerChute, battery/UPS serial number?

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:31 PM . Last Modified: ‎2024-03-20 04:11 AM

0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:31 PM . Last Modified: ‎2024-03-20 04:11 AM

Hi,

What is the serial number of the ES750 and what type of tone are you hearing? Is the tone constant or is the unit beeping?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:31 PM . Last Modified: ‎2024-03-20 04:11 AM

0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:31 PM . Last Modified: ‎2024-03-20 04:11 AM

Serial number is 3B0803X49229.  The tone is constant.  It's fairly loud.  I hear it when I first open the basement door and it is downstairs, around the back and in a closet.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:31 PM . Last Modified: ‎2024-03-20 04:11 AM

0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:31 PM . Last Modified: ‎2024-03-20 04:11 AM

Hi,

A constant tone indicates an over load. A ES750 can only handle a maximum of 450 watt load. What might be happening is when the DVR and or the NAS spins up the draw on the UPS is to great and causes an overload. I recommend decreasing the load and keeping it below 80% capacity. While determining the 80% load you should be sure to take into account the maximum draw of anything attached. DVRs and NAS may draw X wattage while running but quite often draw more when drives are spinning up.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:31 PM . Last Modified: ‎2024-03-20 04:11 AM

0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:31 PM . Last Modified: ‎2024-03-20 04:11 AM

I really hadn't considered that I might be overloading it with only a few devices connected.  Thank you - I will disconnect the dvr and plug it in elsewhere and report back in a week or so.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:31 PM . Last Modified: ‎2024-03-20 04:11 AM

0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:31 PM . Last Modified: ‎2024-03-20 04:11 AM

I researched the draw for each of the devices connected to the ES750 and it doesn't appear that the total doesn't come anywhere near the 450 watts.  I have:

- Synology DS1812+ NAS with 4 3TB Western Digital Red drives installed.

- Directv HR21 DVR

- 1 external AcomData 1TB eSata external hard drive connected to the DVR

- Apple Airport Extreme 5th generation router

- Actiontec DSL modem

- REI HDMI switch

- Canon MP970 multi-function printer

- D-Link 8port gigabit ethernet switch

If all were active at once the draw should be no more than about half the 450 rating.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:32 PM . Last Modified: ‎2024-03-20 04:11 AM

0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:32 PM . Last Modified: ‎2024-03-20 04:11 AM

Since the 24th I left the NAS turned off.  Because it hadn't happened in four days I figured it may have something to do with it.  Today it triggered again.  Constant tone and everything was off except the modem.  Do I have a defective unit?  For most of these items I just need it to work like a surge protector. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:32 PM . Last Modified: ‎2024-03-20 04:11 AM

0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:32 PM . Last Modified: ‎2024-03-20 04:11 AM

How did you verify you're not overloading the unit? That sounds like a lot of stuff. I'll assume you added up the wattage draw?

What this does sound like is an overload shutdown especially if you can turn the unit back on and it passes its self test and operates normally. What I mean by overload shutdown is the UPS tries to go to battery potentially and cannot because its overloaded.

Is it possible to try and simulate this yourself by having this load connected (or a very similar non critical load) and pull the plug on the UPS?

Another idea is to connect the APC USB cable and via PowerChute Personal Edition, verify what the wattage draw is according to the unit and see if anything else of interest appears. This could also help you identify your typical wattage draw and see how close it is to 450 because perhaps periodic increases in load from attached devices are putting it over the edge.

Lastly, I was thinking - how old is the battery - perhaps the UPS is also unable to support the load when the UPS goes on battery. If you can give me the first 6 characters of your UPS serial number, that will tell us the age of the battery/unit assuming the battery is original. If not, let me know when you replaced the battery.

I honestly sometimes find these types of UPSs so simple that it makes it difficult! embarassed

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:32 PM . Last Modified: ‎2024-03-20 04:11 AM

0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:32 PM . Last Modified: ‎2024-03-20 04:11 AM

I suspect the unit is becoming overloaded - I just don't think it should.  Yes - there are a lot of items plugged in but the 750 has the outlets so I assume the expectation is that you would have that many plugged in.  I don't really need the UPS for much.

I did add up the wattage draws and it doesn't get anywhere near 450. 

For most of these items - I just need it to operate like a surge protector.  It shouldn't be shutting down so regularly.  It was fine until the last couple of months and I've not plugged anything else into it.

BTW - when it shuts down it continues to run the dsl modem, but only that.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:32 PM . Last Modified: ‎2024-03-20 04:11 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:32 PM . Last Modified: ‎2024-03-20 04:11 AM

And the DSL modem is connected to a Battery Backup + surge outlet vs. surge only?

Any feedback on my other questions - using PowerChute, battery/UPS serial number?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of