ES 350 restarting PC

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • ES 350 restarting PC
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:39 PM . Last Modified: ‎2024-03-26 12:00 AM

0 Likes
4
881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:39 PM . Last Modified: ‎2024-03-26 12:00 AM

ES 350 restarting PC

Trying to isolate a problem we're having with our APC Back UPS ES. I don't think this is computer-related as it also did it with our Windows PC. I am now running our Powermac G5 off of the APC and, on occasion, the computer will restart on its own, with no evident power outages or surges, etc. I think this happened both when the USB was connected and when it was not. Does this sound like a problem with the unit itself? The battery is apparently at 100% charge, according to the OSX (Energy preference panel). Any ideas?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:39 PM . Last Modified: ‎2024-03-26 12:00 AM

0 Likes
0
881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:39 PM . Last Modified: ‎2024-03-26 12:00 AM

Hi,

What is your configuration like? What's plugged into the UPS and where? Are you using any power strips/extensions before or after the UPS?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:39 PM . Last Modified: ‎2024-03-26 12:00 AM

0 Likes
0
881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:39 PM . Last Modified: ‎2024-03-26 12:00 AM

Macs PSUs and many PSUs are now coming out with Active PFC and these PSUs require a lot of power when they are turned on. Since it takes a few milisencods to go from the energy coming out of the wall outlet to the energy coming out from the battery, you're making the PSU "turn off" for a few miliseconds and then back on again. This can make the PSU draw a lot of power and the UPS may become overloaded. Some PSUs are also very sensitive to the time delay it takes to go to battery power, so I recommend you choosing the Smart UPS series that has a faster battery switching time and produces pure sinewave - some PSU's are also sensitive to approximated sinewave produced by cheap UPSes.

Ithink the least thing you should do now is to buy a more powerfull UPS, since you MAC can draw much more power than your 350VA UPS can deliver.

What is happening in you case is that there is no need for power to completely go out for the UPS to switch to battery. Sags and overvoltages can do this. Some UPSes let you change its sensitivity so it stops going to battery because of small voltage sags. I always let mine at the lowest setting, since all my PSUs can deal with more severe voltage sags.

Message was edited by: rau

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:39 PM . Last Modified: ‎2024-03-26 12:00 AM

0 Likes
0
881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:39 PM . Last Modified: ‎2024-03-26 12:00 AM

Macs I find are a lot more like servers - thus they can reboot when they see the step approximated sine wave that is outputted by the Back UPS line while on battery. Some also dont like the transfer time to battery which for this model is somewhere around 4-6 or 8 ms or so.

For servers, and high end macs, we usually recommend - like Rau said, something with more VA - usually a minimum of 800VA I'd say and certain mac's will require a pure sinewave output (like a wall outlet provides) and a lower transfer time to battery - 2-4ms or even 0ms.

Our Smart UPS line outputs a pure sinwave, has ALL battery+surge protection outlets and has a transfer time to battery of 2-4ms.

You can view them here but as you can see, they are a bit more expensive.

Some mac's need a smart ups, others can deal with it. So at a minimum, I'd try something with more VA in the Back UPS line - maybe a BR800BLK model or BR1200.

The ES 350 you have only provides ~200 watts.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:39 PM . Last Modified: ‎2024-03-26 12:00 AM

0 Likes
0
881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:39 PM . Last Modified: ‎2024-03-26 12:00 AM

One note about Macs: While any of the Power Mac or Mac Pro tower form-factor PCs are high-end, workstation/server class professional computers, other Macs like the iMac (any generation/form factor) or Mac mini have power requirements similar to the average home PC.

It's very common for customers with the Power Mac or Mac Pro systems to report difficulties with their APC Back-UPS. This is to be expected since these computers often do use PFC and usually overload smaller Back-UPS units. This is similar to the issue we're seeing in this discussion.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:39 PM . Last Modified: ‎2024-03-26 12:00 AM

0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:39 PM . Last Modified: ‎2024-03-26 12:00 AM

Hi,

What is your configuration like? What's plugged into the UPS and where? Are you using any power strips/extensions before or after the UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of