Current flow in a home power installation

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Current flow in a home power installation
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:20 PM . Last Modified: ‎2024-03-21 03:47 AM

0 Likes
5
1336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:20 PM . Last Modified: ‎2024-03-21 03:47 AM

Current flow in a home power installation

In a typical home power delivery scenario, there is distribution transformer with two oppositely phased hot conductors and a center tap neutral. The home's 110v loads are connected across either hot conductor and the neutral. When (simultaneously) one of the hot conductors is in the positive state and the other is in the negative state, how can the current flow both out of the neutral connector into the more negatively charged hot conductor and into the neutral from the more positively charged hot conductor, at the same instant? What is actually going on?

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:21 PM . Last Modified: ‎2024-03-21 03:47 AM

0 Likes
0
1336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 PM . Last Modified: ‎2024-03-21 03:47 AM

In a typical home power delivery scenario, there is distribution transformer with two oppositely phased hot conductors and a center tap neutral. The home's 110v loads are connected across either hot conductor and the neutral. When (simultaneously) one of the hot conductors is in the positive state and the other is in the negative state, how can the current flow both out of the neutral connector into the more negatively charged hot conductor and into the neutral from the more positively charged hot conductor, at the same instant? What is actually going on?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:20 PM . Last Modified: ‎2024-03-21 03:47 AM

0 Likes
0
1336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:20 PM . Last Modified: ‎2024-03-21 03:47 AM

If you've got 2 hots180 degrees out of phase and a neutral, the current will only flow one way on the neutral. If for instance you have 10 amps on 1 circuit and 5 on the other, the neutral will only have 5 amps on it. Let's say that current flows from positive to negetive (some people say it is negative to positive or hole flow). Let's also say that you have circuits A and B and for this 120th of a second, the hot leg feeding B is positive, they share a neutral, and they're 180 degrees out of phase. The load on B is drawing 10 amps. The load on A is drawing 5 amps. With respect to B's hot leg, neutral is negative. 10 amps of curent are flowing on B's hot and 5 are returning down the neutral. The other 5 amps are flowing from that neutral point to A's hot leg as it's load is using 5 amps.

If both circuits were drawing 10 amps, there would actually be no current on the neutral.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:20 PM . Last Modified: ‎2024-03-21 03:47 AM

0 Likes
0
1336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:20 PM . Last Modified: ‎2024-03-21 03:47 AM

I am confused about the last sentence. You said if both circuits were drawing 10 amps, there was no current on the neutral. Let's say you took the neutral away and the two individual ten amp loads were then in series, they wouldn't draw 10 amps. So how are they each drawing 10 amps if the neutral is there but not really doing anything?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:20 PM . Last Modified: ‎2024-03-21 03:47 AM

0 Likes
0
1336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:20 PM . Last Modified: ‎2024-03-21 03:47 AM

Let's say you have 2 loads. Each one is drawing 1200 watts exactly (12 ohms). One of these loads on a 120 volt circuit will draw exactly 10 amps. 2 of these loads in series (2400 watts) on a 240 volt circuit will still draw 10 amps.

(2) 12 ohm loads in series = 24 ohms.

P = E 2 / R
or
wattage = voltage squared divided by resistance.
P = 240 squared / 24.
P = 57,600 / 24.
P = 2400.

I = P / E
or
Current = Wattage / Voltage
! = 2400 / 240
I = 10

You still have 10 amps.
I found a nice little ohms law calculator if you'd like:
http://www.the12volt.com/ohm/page2.asp#resistance

I found another link today that may help with both this question and your grounding question.
http://www.tkk.fi/Misc/Electronics/wire_mains.html
This has quite a bit of information for you. One of the sections within this document also references the shared neutral aspect of this question:
http://dotznize.com/electric/?a=sh
Similar to what I mentioned in my last response, this document says:
The answer is that the neutral does not carry the sum of the two currents; it carries the difference. If both loads draw the same amount of current, the neutral will carry no current

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:21 PM . Last Modified: ‎2024-03-21 03:47 AM

0 Likes
0
1336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 PM . Last Modified: ‎2024-03-21 03:47 AM

With or without a Neutral, the voltage drop in the middle of the 2 equal loads will be 1/2 of the total voltage across the 2. When you have multiple light bulbs plugged into the same circuit, they are actually connected in parallel and each will have the same voltage across it. if you took 2 120 volt light bulbs, connected them in series, and put 240 volts across the 2 of them, you would get a 120 volt measurement from the wire in the middle to either of the 2 hot legs.

Using calculations from before, we know that there is 10 amps total. We also know that there was 12 ohms per load. (2) 12 amp loads in series adds their resistance for a total of 24 ohms. Across 240 volts, that was 2400 watts and 10 amps. Using that same ohm's law that states 10 amps across a 24 ohm load is 240 volts, by that same math, 10 amps across a 12 amp load is 120 volts.

http://www.techlearner.com/DCPages/DCReseries.htm

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:21 PM . Last Modified: ‎2024-03-21 03:47 AM

0 Likes
0
1337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 PM . Last Modified: ‎2024-03-21 03:47 AM

In a typical home power delivery scenario, there is distribution transformer with two oppositely phased hot conductors and a center tap neutral. The home's 110v loads are connected across either hot conductor and the neutral. When (simultaneously) one of the hot conductors is in the positive state and the other is in the negative state, how can the current flow both out of the neutral connector into the more negatively charged hot conductor and into the neutral from the more positively charged hot conductor, at the same instant? What is actually going on?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore