Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82548members
350159posts

Current flow in a home power installation

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
iamsand_apc
Crewman
Crewman
0 Likes
5
169

Current flow in a home power installation

This was originally posted on APC forums on 5/30/2007


In a typical home power delivery scenario, there is distribution transformer with two oppositely phased hot conductors and a center tap neutral. The home's 110v loads are connected across either hot conductor and the neutral. When (simultaneously) one of the hot conductors is in the positive state and the other is in the negative state, how can the current flow both out of the neutral connector into the more negatively charged hot conductor and into the neutral from the more positively charged hot conductor, at the same instant? What is actually going on?


Accepted Solutions
iamsand_apc
Crewman
Crewman
0 Likes
0
169

Current flow in a home power installation

This was originally posted on APC forums on 5/30/2007


In a typical home power delivery scenario, there is distribution transformer with two oppositely phased hot conductors and a center tap neutral. The home's 110v loads are connected across either hot conductor and the neutral. When (simultaneously) one of the hot conductors is in the positive state and the other is in the negative state, how can the current flow both out of the neutral connector into the more negatively charged hot conductor and into the neutral from the more positively charged hot conductor, at the same instant? What is actually going on?

See Answer In Context

5 Replies 5
BillP
Administrator Administrator
Administrator
0 Likes
0
169

Re: Current flow in a home power installation

This reply was originally posted by Steve on APC forums on 5/30/2007


If you've got 2 hots180 degrees out of phase and a neutral, the current will only flow one way on the neutral. If for instance you have 10 amps on 1 circuit and 5 on the other, the neutral will only have 5 amps on it. Let's say that current flows from positive to negetive (some people say it is negative to positive or hole flow). Let's also say that you have circuits A and B and for this 120th of a second, the hot leg feeding B is positive, they share a neutral, and they're 180 degrees out of phase. The load on B is drawing 10 amps. The load on A is drawing 5 amps. With respect to B's hot leg, neutral is negative. 10 amps of curent are flowing on B's hot and 5 are returning down the neutral. The other 5 amps are flowing from that neutral point to A's hot leg as it's load is using 5 amps.

If both circuits were drawing 10 amps, there would actually be no current on the neutral.

iamsand_apc
Crewman
Crewman
0 Likes
0
169

Re: Current flow in a home power installation

This was originally posted on APC forums on 6/2/2007


I am confused about the last sentence. You said if both circuits were drawing 10 amps, there was no current on the neutral. Let's say you took the neutral away and the two individual ten amp loads were then in series, they wouldn't draw 10 amps. So how are they each drawing 10 amps if the neutral is there but not really doing anything?

BillP
Administrator Administrator
Administrator
0 Likes
0
169

Re: Current flow in a home power installation

This reply was originally posted by Steve on APC forums on 6/4/2007


Let's say you have 2 loads. Each one is drawing 1200 watts exactly (12 ohms). One of these loads on a 120 volt circuit will draw exactly 10 amps. 2 of these loads in series (2400 watts) on a 240 volt circuit will still draw 10 amps.

(2) 12 ohm loads in series = 24 ohms.

P = E 2 / R
or
wattage = voltage squared divided by resistance.
P = 240 squared / 24.
P = 57,600 / 24.
P = 2400.

I = P / E
or
Current = Wattage / Voltage
! = 2400 / 240
I = 10

You still have 10 amps.
I found a nice little ohms law calculator if you'd like:
http://www.the12volt.com/ohm/page2.asp#resistance

I found another link today that may help with both this question and your grounding question.
http://www.tkk.fi/Misc/Electronics/wire_mains.html
This has quite a bit of information for you. One of the sections within this document also references the shared neutral aspect of this question:
http://dotznize.com/electric/?a=sh
Similar to what I mentioned in my last response, this document says:
The answer is that the neutral does not carry the sum of the two currents; it carries the difference. If both loads draw the same amount of current, the neutral will carry no current

BillP
Administrator Administrator
Administrator
0 Likes
0
169

Re: Current flow in a home power installation

This reply was originally posted by Steve on APC forums on 6/4/2007


With or without a Neutral, the voltage drop in the middle of the 2 equal loads will be 1/2 of the total voltage across the 2. When you have multiple light bulbs plugged into the same circuit, they are actually connected in parallel and each will have the same voltage across it. if you took 2 120 volt light bulbs, connected them in series, and put 240 volts across the 2 of them, you would get a 120 volt measurement from the wire in the middle to either of the 2 hot legs.

Using calculations from before, we know that there is 10 amps total. We also know that there was 12 ohms per load. (2) 12 amp loads in series adds their resistance for a total of 24 ohms. Across 240 volts, that was 2400 watts and 10 amps. Using that same ohm's law that states 10 amps across a 24 ohm load is 240 volts, by that same math, 10 amps across a 12 amp load is 120 volts.

http://www.techlearner.com/DCPages/DCReseries.htm

iamsand_apc
Crewman
Crewman
0 Likes
0
170

Current flow in a home power installation

This was originally posted on APC forums on 5/30/2007


In a typical home power delivery scenario, there is distribution transformer with two oppositely phased hot conductors and a center tap neutral. The home's 110v loads are connected across either hot conductor and the neutral. When (simultaneously) one of the hot conductors is in the positive state and the other is in the negative state, how can the current flow both out of the neutral connector into the more negatively charged hot conductor and into the neutral from the more positively charged hot conductor, at the same instant? What is actually going on?