Critical Alarms Present Self-Test Failed Battery Charger Fault
  • Critical Alarms Present Self-Test Failed Battery Charger Fault
2151
121
Posted: ‎2021-06-28 06:35 AM . Last Modified: ‎2024-03-26 11:32 PM
Hey,
I have a APC Smart UPS :
Model: Smart-UPS 3000
Serial Number:
Firmware Revision: UPS 07.1 / MCU 05.0 / UBL 7.20 / MBL 05.0 (ID17)
Manufacture Date: 12/02/2011
Apparent Power Rating: 3000 VA
Real Power Rating: 2700 W
After installing new battery's i have 2 critical alarms ... Present Self-Test Failed and Battery Charger Fault ?
If i take a look at 'Detailed Status/Measurements' everything looks fine ...
Last Battery Transfer: UPS battery test
Internal Temperature: 30.6°C
Runtime Remaining: 1hour 20min
UPS Input
Input Voltage: 237.6 VAC @ 50.0 Hz
UPS Output
Output Voltage: 237.6 VAC @ 50.0 Hz
Load Current: 2.2 Amps
Output VA: 16.2 %
Output Watts: 13.6 %
Output Efficiency: 97.0 %
Output Energy Usage: 19547.90 kWh
Battery Status
Battery Capacity: 100.0 %
Battery Voltage: 58.0 VDC
What do i have to do for fixing the problems ? Thx to all 😉
* I have already done a firmware update and a reboot of the ups but noting is changing ?!
Replies 0