Crickets in my Back-UPS XS 1300

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Crickets in my Back-UPS XS 1300
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 04:47 AM . Last Modified: โ€Ž2024-03-22 12:28 AM

0 Likes
6
1821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:47 AM . Last Modified: โ€Ž2024-03-22 12:28 AM

Crickets in my Back-UPS XS 1300

I have two Back-UPS XS 1300LCD units sidding side by side on my desk that have been in place there since 01/28/2008. There's not a lot of draw on the unit (typically 1-2watts) that is making a very high pitch chirping every couple of seconds (a cricket like noise that is not very loud, but very annoying) It is a regularly paced cyclic noise. There are no error messages on the LED panel, but it does show 254 events in the counter. I do not have the unit connected to a USB on a computer it is just providing power to a telephone and some times a computer if I turn that particular computer on.

I tried cycling power to the unit using the front panel power button and did get it to shut off and that made the pitch to change slightly when I turned it back on, but there was no change in general behavior noted.

What is the cause of this annoying noise ?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 04:48 AM . Last Modified: โ€Ž2024-03-22 12:27 AM

0 Likes
0
1819
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:48 AM . Last Modified: โ€Ž2024-03-22 12:27 AM

I have the same problem. It's making noise even with each of two new batteries. Clip of the noise is in the first post here: [http://forums.apc.com/spaces/4/back-ups-surge-protectors/forums/general/3824/battery-not-holding-ful...]

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 04:47 AM . Last Modified: โ€Ž2024-03-22 12:28 AM

0 Likes
0
1820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:47 AM . Last Modified: โ€Ž2024-03-22 12:28 AM

On the LCD display, do you see any icon that is flashing?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 04:47 AM . Last Modified: โ€Ž2024-03-22 12:27 AM

0 Likes
0
1820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:47 AM . Last Modified: โ€Ž2024-03-22 12:27 AM

There are no flashing indicators on the UPS LED panel - No reports of any problems from Powerchute connected to the UPS with the USB cable. I'm starting to suspect it is marginal batteries and some sort of failing beep alert (the UPS internal beeper being the failing component) although the lack of any failure reports from the Powerchuteware when it runs it diagnostic sort of cancels that idea.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 04:48 AM . Last Modified: โ€Ž2024-03-22 12:27 AM

0 Likes
0
1820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:48 AM . Last Modified: โ€Ž2024-03-22 12:27 AM

Do you see this happening on those two UPS?

If you have PowerChute Personal Edition installed can you click on Performance (this is under the Monitor Sysstem section) and from there you could see the different power problem that the UPS has encountered. Also, let us try to change the sensitivity to Low settings. Would it be possible for you to record the sound?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 04:48 AM . Last Modified: โ€Ž2024-03-22 12:27 AM

0 Likes
0
1820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:48 AM . Last Modified: โ€Ž2024-03-22 12:27 AM

Hi

These noises just sound like the switch mode power supplies inside recharging/float charging the battery. My Backup Pro 550 makes the same noises.

Is it worse or a different frequency of chirping after you self-test or simulate a power failure? If yes that is almost certainly normal even if you find it annoying.

Regards

Phil

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 04:48 AM . Last Modified: โ€Ž2024-03-22 12:27 AM

0 Likes
0
1820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:48 AM . Last Modified: โ€Ž2024-03-22 12:27 AM

Problem resolved, basically identified as dying battery - replaced the battery pack with new batteries and the noise has ceased. Powerchute was basically worthless far as trying to find the original problem.

Tried the pushing of the front panel buttons and it sort of disrupted the chirp when it went from on-line to off and back to on-line, The pitch shifted a little, but a short time later it was back to the same old faint hi-pitch chirp.

The disappearance of the chirping points back to the earlier thought that it was the battries dying causing the UPS internal 'tronic's to squack, even though the battries weren't bad enough to set off major alarms.

One thing that helped really seal the deal on battery replacement was pulling the UPS out of the wall and having the suspect one drop dead - a second same model UPS sitting next tot he dead one (that was put in service at the same time) also showed extreme lameness with a very short on-battery run time before also going belly up...

Do not know if any of the mics I have would have been able to pick up the sound with a fidelity that would have made it audible. If you ever had a hearing test and recall the higher frequency end of the tests - that's pretty close to what this sounded like (only pulsing) - nothing "normal" about that sound coming from an electronic device - any sound like that indicates a failing component/circuit/power flow, unless it is a hear test sound generator ๐Ÿ˜‰

Thanks for trying to assist just the same !

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 04:48 AM . Last Modified: โ€Ž2024-03-22 12:27 AM

0 Likes
0
1820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 04:48 AM . Last Modified: โ€Ž2024-03-22 12:27 AM

I have the same problem. It's making noise even with each of two new batteries. Clip of the noise is in the first post here: [http://forums.apc.com/spaces/4/back-ups-surge-protectors/forums/general/3824/battery-not-holding-ful...]

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of